• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Rated walls

Hang on.... depends on why the rated wall exists. If a fire wall is used to create separate buildings or a fire barrier is used to reduce fire area, then rating is higher.

Fire wall would be 3hrs per Table 706.4

Fire barrier would also be 3hrs per Table 707.3.10
 
I would double check the type of construction given that type 1 construction requires either a 1 or 1 1/2 hour rated roof assembly for the F-1 occupancy.
 