• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

10 awg wire on 50A breaker

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,041
Location
Somewhere Too Hot & Humid
Is it possible that this is actually allowed and is compliant? If so, under what circumstances can we have a 10 awg wire on a 50A breaker?

IMG_5428.JPG
 
I know enough to troubleshoot basic stuff and to also know I'll probably kill myself if I ever poke around a 3-phase system.

Assuming the condenser example- if 10 awg wire can carry 40 amps (at 90 degrees C per Wikipedia chart on AWG), wouldn't the wire be a fire risk if it actually pulled 50 amps? Or would the disconnect at the condenser be fused lower and all is right and compliant?
 
I know enough to troubleshoot basic stuff and to also know I'll probably kill myself if I ever poke around a 3-phase system.

Assuming the condenser example- if 10 awg wire can carry 40 amps (at 90 degrees C per Wikipedia chart on AWG), wouldn't the wire be a fire risk if it actually pulled 50 amps? Or would the disconnect at the condenser be fused lower and all is right and compliant?

Great question. Actually, #10 copper is only good for 30A. You can only use the 90deg column in certain circumstances. For motors, in most cases, the circuit breaker is only used for short circuits and ground faults and would trip. The real issue with wire size vs breaker is the ability of the wire to handle normal loads.

You may want to see the thread I posted about circuits for motors. You can click here: https://www.thebuildingcodeforum.co...ductors-and-overload-short-circuit-gfp.26518/
 