An alternative to post-tension?
Forum Coordinator
Somewhere Too Hot & Humid
This does have an ICC-ES report and it looks rather interesting. I don't know about testing for seismic areas. Your thoughts?
DELTABEAM® is a superior composite beam enabling slim-floors for multi-story buildings of any type, whether low-rise or high-rise. Its composite action between steel and concrete allows for creative structures with large open spaces.
Underwriter laboratories (UL) fire tests have proven DELTABEAM® has excellent fire resistance without any additional protection. Its shallow design decreases a building’s floor-to-floor height while eliminating conflicts with HVAC systems.
https://www.peikkousa.com/products/deltabeam-slim-floor-structures/overview/
Doesn't appear to be approved for California yet and requires more colums given 27" span limit,
Parking structures vs hotel uses or not?
Might bounce a lot.
I didnt see that. Seems awfully short. I did see a comment on thd opening page that it can span 30 ft.
ADAguy ... re-read what you typed. 27 inch span. Thats the same as a 5/4 deck board.
https://www.peikkousa.com/products/deltabeam-slim-floor-structures/technical-information/
15 to 55 feet in length 20 to 40 ft clear span
TABLE NOTES
Top Left Corner (green): DELTABEAM® Span (ft) with 50 psf Live Load
Bottom Right Corner (blue): DELTABEAM® Span (ft) with 100 psf Live Load
2” Topping and 30 psf miscellaneous superimposed dead load assumed for all cases.
50 PSF LL seems a bit light to support furniture and moving traffic as in humans and cars.
Check out IBC T1607.1... 50psf is the specified LL for offices.
Definitely not intended for a garage application (i.e. supporting cars).
2018 IBC
14. Garages (passenger vehicles only) is 40 psf
Note "a" concentrated load and note "o"
a. Floors in garages or portions of buildings used for the storage of motor vehicles shall be designed for the uniformly distributed live loads of this table or the following concentrated loads: (1) for garages restricted to passenger vehicles accommodating not more than nine passengers, 3,000 pounds acting on an area of 41/2 inches by 41/2 inches; (2) for mechanical parking structures without slab or deck that are used for storing passenger vehicles only, 2,250 pounds per wheel.
o. Live load reduction is only permitted in accordance with Section 1607.11.1.3 or Item 2 of Section 1607.11.2.