• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Electrical Service Approval

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,049
Location
Somewhere Too Hot & Humid
Assuming the load calculations are good, based on what you see here, do you have enough/correct information to approve this riser diagram for the service?

Screen Shot 2019-08-24 at 14.04.54.png
 
Unable to approve this service as submitted, more detail is needed. It appears that service conductors to the main switch and feeders from the main switch are sharing the same 'New Wireway', this is not permitted per NEC 230.7.
 
Unable to approve this service as submitted, more detail is needed. It appears that service conductors to the main switch and feeders from the main switch are sharing the same 'New Wireway', this is not permitted per NEC 230.7.

I agree. Once we have more information we can then determine the size of the GEC. Yes, the way they are showing the new wireway, they will definitely be in violation of 230.7. I am also curious as to where they will terminate the GEC (I suspect they will terminate it to the gutter which will be another problem). It is just a bad design.
 