• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Mechanical Room Ratings B use, VB construction

Hyrax4978

Registered User
Joined
Nov 28, 2016
Messages
205
Location
Hartford, CT
I have a renovation to a commercial building of type 5B construction that is just about wrapping up. The local building official said he "thought" the mechanical room had to be rated. I don't see anywhere that it says that. checked with the mechanical engineer also and he agreed that he didn't see anyplace it would need to be rated in the code. When we asked the B.O. for a code section and he didn't have one the building official asked for a letter signed and stamped that stating the mechanical room definitely does not need to be rated. We have a 10 ton, electric air handler so there is no combustion in the mechanical room.

Am i missing something. I don't see anyplace in the code to trigger rating the room. Anyone else out there find a place to require the mechanical room to be rated with this type of equipment in there.
CT 2018 which is based on the IBC 2015.

Thank you!
 
And not part/ attached to a rated corridor ??

Does the building have a fire sprinkler system?

My thinking would be no,,,,, and all that a/c info is shown on the plans???
 
The mechanical room is not attached to any rated corridors. its on the side of the building to allow for fresh air. It is surrounded on three sides by offices and a short non rated corridor. None of the duct work penetrates this tenant space.
 
Incidental use would be the only thing.....Sprinklers would typically make it go away...

Furnace room where any piece of equipment is over 400,000 Btu per
hour input
1 hour or provide automatic sprinkler system

Rooms with boilers where the largest piece of equipment is over 15 psi and 10 horsepower
1 hour or provide automatic sprinkler system

Refrigerant machinery room 1 hour or provide automatic sprinkler system

Tell the BO there already is such paperwork...It's called the approved plans.....
 
  • Like
Reactions: cda
Thank you Steveray, I checked the incidental uses early in design. Don't trigger the rating there.

I agree, its like the B.O. wants something that isn't required, but since its not required and we don't want to do it, he says he feels it "should be" and if we don't want to we need to certify against it. so when he said that it made me question if i missed something else. PIA!
 
Sounds like he is an idiot just looking for a CYA instead of doing his job.....No offense, because I know you are a designer, but letting a designer "self certify" is at best, dumb, and probably illegal for the BO to do....

If that is the case we can save a lot of money on plans and BO salary if you just write a letter that you are going to build it to code, and then a letter that you did...
 
  • Like
Reactions: cda
Dear Sir,

Contrary to popular belief the Code does not require, what the code does not require.

Thank you, please issue green tag.
 
If he is old school the requirement for a fire separation for a " Heating Equipment Room" (UBC) however if he never looked any further in the code at the exception for 40,000 btu equipment then in his mind something is missing
 
Not required as far as I am aware. Perhaps there may be an NEC requirement if there are panels or other electrical equipment in the room.
 
Incidental use would be the only thing.....Sprinklers would typically make it go away...
Furnace room where any piece of equipment is over 400,000 Btu per
hour input
1 hour or provide automatic sprinkler system
Rooms with boilers where the largest piece of equipment is over 15 psi and 10 horsepower
1 hour or provide automatic sprinkler system
Refrigerant machinery room 1 hour or provide automatic sprinkler system
Tell the BO there already is such paperwork...It's called the approved plans.....


As stated by steveray Section 509 Incidental Use

TABLE 509- INCIDENTAL USES

Furnace rooms where any piece of equipment is over 400,000 Btu per.
Note not combined BTU/h or all the equipment, any piece of equipment over 400,000 Btu per
hour input, requires a seperation.
 
Sounds like he is an idiot just looking for a CYA instead of doing his job.....No offense, because I know you are a designer, but letting a designer "self certify" is at best, dumb, and probably illegal for the BO to do....

If that is the case we can save a lot of money on plans and BO salary if you just write a letter that you are going to build it to code, and then a letter that you did...

Would suggest you check with your E & O carrier before even considering this as it exceeds what the plans call for which is "compliance with codes and regulations".
 