Dan Helphrey
Registered User
Here is the condition: No part of the building is required to be rated per 2018 IBC or IFC, however it is an Owner requirement that we comply with NFPA 75. NFPA 75 requires the data equipment room to be rated.
Here is the question: The data room exits to a corridor system, which would not otherwise need to be rated (U occupancy, sprinklered, very low occupant load). Does the required rating of the equipment room trigger a requirement to maintain the same rating for the entire egress path? Does it make a difference that NFPA 75 is a voluntary standard?
Thanks!
Here is the question: The data room exits to a corridor system, which would not otherwise need to be rated (U occupancy, sprinklered, very low occupant load). Does the required rating of the equipment room trigger a requirement to maintain the same rating for the entire egress path? Does it make a difference that NFPA 75 is a voluntary standard?