• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Junction box for extending feeder to move main panel

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,041
Location
Somewhere Too Hot & Humid
For a Level 2 renovation of a condo in a type II building they moved some walls and now the main panel requires a junction box that transitions from EMT that was using the EMT as the equipment grounding conductor EGC. In order to extend it they P-Tapped the 3 conductors and added a bonding bushing to the EMT entering the PVC JB in order to provide the continuance of the EGC to the new/moved main panel. Again, this is a feeder to a main panel, not service conductors. Thoughts other than an access panel in the middle of the ceiling?
IMG_6633.JPG
 
That box doesn't look like it meets the requirements of 314.28.

Well that was quick.... LOL.
You are correct, it does not. I think the owner won't be happy either about 314.29. They should have pulled a new feeder with a ground. Who wants a big access panel in the middle of a ceiling anyway?

IMG_6634.JPG
 
J-box, not the panel...
Right. Ok, looking at the original picture, no screws visible, I’m guessing the jbox is held tight to the ceiling by the nut on the embedded conduit. So the horizontal conduit is supported by the shims on the ceiling framing. Very professional.
 