Picture a "penthouse" room for 76 occupants on top of an art gallery flat roof (with parapets) that is open-to-the-sky. Let's say the gallery roof is 80'x 100' and the penthouse is 40'x60' in the middle of that roof. There are exit stairs at either end of the roof. The gallery roof footprint is less than 10' away from the property lines on all sides.
When a person leaves the penthouse, they walk across the middle of the roof deck to get to the stairs. Based on occupant load the required exit width is 44", but of course we have 80' width of roof to walk on, so that's not problem.
Q1. Does that egress description make the roof an "Egress Balcony" for the penthouse per 2016 CBC/IBC 1021.1?
Q2. If "yes", then 1021.4 says that exterior egress balconies shall have min 10' fire separation from adjacent lot lines, as measured from the exterior edge of the egress balcony. Question: if our roof is 80' wide and we only need 44" (or 48" for ADA) of path down the middle of the roof, then do I have to measure from the PL to the outermost edge of the roof? Or can I measure from the PL to the required width of the egress balcony?
When a person leaves the penthouse, they walk across the middle of the roof deck to get to the stairs. Based on occupant load the required exit width is 44", but of course we have 80' width of roof to walk on, so that's not problem.
Q1. Does that egress description make the roof an "Egress Balcony" for the penthouse per 2016 CBC/IBC 1021.1?
Q2. If "yes", then 1021.4 says that exterior egress balconies shall have min 10' fire separation from adjacent lot lines, as measured from the exterior edge of the egress balcony. Question: if our roof is 80' wide and we only need 44" (or 48" for ADA) of path down the middle of the roof, then do I have to measure from the PL to the outermost edge of the roof? Or can I measure from the PL to the required width of the egress balcony?