• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Cutting the bottom of a fire-rated door

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
10,975
Location
Somewhere Too Hot & Humid
If a fire rated door must be cut to make room for new, much higher tile, can it be legally done?

Would a letter from the manufacturer's engineer suffice or would testing be required?
 
From the "la puerta" guru



NFPA 80 specifically allows the following preparations to be made on the job site:

  • Holes for surface-applied hardware
  • Function holes for mortise locks
  • Holes for labeled viewers
  • A maximum 3/4-inch undercutting of wood and composite doors (verify this with the door manufacturer before modifying the door)
  • Installation of protection plates

https://idighardware.com/2018/12/qq-job-site-preps-for-fire-doors/
 