• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Evacuation Signs - Sections 403 & 404

Dominic

SAWHORSE
Joined
Jun 20, 2017
Messages
49
Location
Albany
We typically renovate older high-rise buildings that have evacuation signs on the back of the apartment doors. We review the old plan with the owner and fire department and install new signs.

In reading 403 and 404, it says that we need to develop an evacuation plan but it only has to be distributed to the tenants.

Is there some place in the code that requires it to be permanently installed?
 
Should have added

AHJ and FD May want a copy,,, ask

If a fire command room more than likely copy there
 
2018 IFC
R-2 requirements
403.10.2.2.1 Guide contents.
A fire emergency guide shall describe the location, function and use of fire protection equipment and appliances available for use by residents, including fire alarm systems, smoke alarms and portable fire extinguishers. Guides shall include an emergency evacuation plan for each dwelling unit.
403.10.2.2.2 Emergency guide maintenance.
Emergency guides shall be reviewed and approved by the fire code official.
403.10.2.2.3 Emergency guide distribution.
A copy of the emergency guide shall be given to each tenant prior to initial occupancy
.
403.10.2.3 Evacuation diagrams for dormitories.
A diagram depicting two evacuation routes shall be posted on or immediately adjacent to every required egress door from each dormitory sleeping unit
. Evacuation diagrams shall be reviewed and updated as needed to maintain accuracy.
 