• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Grouted Penetrations

Phil B

SAWHORSE
Joined
Sep 15, 2018
Messages
128
Location
Florida
The building code (Chapter 7) allows full thickness grout or mortar for 6" max pipe penetrations through concrete or masonry walls in order to maintain the fire rating. It appears that a UL design is NOT required: is that correct?
 
That is correct. If you comply with the prescriptive method in the code, then a tested assembly is not required.
 