• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Does lobby need to be fireproofed if egress stair leads to it?

gnarkill283

Registered User
Joined
Nov 15, 2017
Messages
107
Location
New York
Like the title says, I have a egress stair's exit door opening into a lobby. Does that lobby need the same fire rated enclosure as the stair?
 
Look in 1028...

1028.1 General. Exits shall discharge directly to the exterior
of the building. The exit discharge shall be at grade or shall
provide a direct path of egress travel to grade. The exit discharge
shall not reenter a building. The combined use of
Exceptions 1 and 2 shall not exceed 50 percent of the number
and minimum width or required capacity of the required
exits.
Exceptions:
1. Not more than 50 percent of the number and minimum
width or required capacity of interior exit
stairways and ramps is permitted to egress through
areas on the level of discharge provided all of the
following conditions are met:

1.1. Discharge of interior exit stairways and
ramps shall be provided with a free and
unobstructed path of travel to an exterior
exit door and such exit is readily visible
and identifiable from the point of termination
of the enclosure.
1.2. The entire area of the level of exit discharge
is separated from areas below by
 
I don't know what code edition you're under, but the 2018 IBC, Section 1028.1, Exception 1, allows up to 50% of the exit stairways and ramps to discharge at the level of exit discharge provided that all four of the conditions provided are met:
  1. Free and unobstructed path to an exterior exit that is readily visible.
  2. The entire level of exit discharge is separated from any floor levels below with a fire-resistance rating equal to the stair enclosure.
  3. The path from the stair to the exterior exit shall be sprinklered throughout. Areas of the level of exit discharge with access to the same path must either be sprinklered or separated from the path with fire barriers having a fire-resistance rating equal to the stair enclosure.
  4. Exit stairs and exit access stairs that serve the same level and discharge at the same level must be separated by a distance of 30 feet but not less than 1/4 of the overall diagonal of the building.
 
New building. It is a ground floor lobby with no floors below and takes 50% of the occupants so therefore no fireproofing required in the lobby right?
 
New building. It is a ground floor lobby with no floors below and takes 50% of the occupants so therefore no fireproofing required in the lobby right?
Is the entire first story (level of exit discharge) sprinklered? If so, then no additional fire-resistive assemblies are required.
 
  • Like
Reactions: cda
Is the entire first story (level of exit discharge) sprinklered? If so, then no additional fire-resistive assemblies are required.

Ok I recognize 1028 now, been a few days

I am good