• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

House over 600m2

casafras

Registered User
Joined
Jul 29, 2020
Messages
2
Location
ontario
Hey Everyone,

I recently submitted large house for a permit (over 600m2 building area) The plans examiner noted that because the building area exceeds 600m2 it falls outside of part 9 and will fall under part 3 , he then noted I will need a firewall to keep it as a part 9 building.

All our drawings have been reviewed and stamped by a professional engineer.

I have submitted many applications in excess of the 600m2 and not been asked to put in a fire wall.

Question why cant it be a part 3 building?

I am registered and qualified with 'house and 'small buildings'
 
Welcome

There is only one maybe two that speak Canadian

And since up north will not put the code online, a little hard to help neighbors to the north.

Give it a few days for an answer
 
Welcome

There is only one maybe two that speak Canadian

And since up north will not put the code online, a little hard to help neighbors to the north.

Give it a few days for an answer
Thank you for your reply :) I knew I was reaching posting on here.. just looking to see if anyone else has came across this issue.

The Ontario (canada) Building code can be found via this link ;
https://www.ontario.ca/laws/regulation/120332
 
As a broad explanation and to help our American friends understand what is going on,

The Canadian codes (excluding Quebec) are all built off of the structure of the National Building Code. There are largely two sections that a building can be: Part 3 or Part 9 Parts 4,5,6,7, & 8 can apply to any building, but if a building is a Part 3 building, you use Part 3 and vice versa for Part 9. Think of Part 3 as the IBC and Part 9 as the IRC...Kind of...

Occupancy and size determines what part a building must be constructed to.

Part 3
-Post disaster buildings
-assembly occupancies
-care, treatment, and detention occupancies
-high hazard industrial occupancies
Part 3 if over 600 square meters or more than 3 storeys
-residential (does not matter if it is one suite or multiple)
-business and personal services
-mercantile
-low and medium hazard industrial

It is important to point out that the maximum of 600 square meters is based on the defined term of "building area", which is the greatest horizontal area above grade of a single storey (you do not add all the areas on all storeys together).

Some designers will utilize a firewall to reduce the building area. The function of a firewall it to break a single building into two buildings. This can take a single building from Part 3 and make it into two Part 9 buildings, alternatively it is routinely used to try and avoid sprinkler requirements.

So, if the house is over 600 square meters on the largest storey, it is a Part 3 building and needs the involvement of architects and engineers. Alternatively, a firewall could be designed by an engineer to separate the building into two to reduce the requirements.

The qualification refers to the Ontario Building Officials Association.
Housing is for review and inspection of one and two unit dwellings
Small Buildings is everything else in Part 9
Large Buildings is everything in Part 3

This certification stream is shared among many other building official associations across Canada through the Alliance of Canadian Building Official Associations to enable job mobility.
 
So if the total size is more than 600 sm but it’s two or more floors ... it could be a Part 9?
 
does sprinklers matter?
No.

No Part 9 building is required to be sprinklered. A Part 3 building may be required to be sprinklered based on building area and number of storeys. Sometimes it can also come down to fire fighter access routes, but not typical outside of urban cores.

Sprinkles may still be seen in some buildings even where not required based on relaxations in life safety system requirements though.

Part 9 buildings are designed to get everyone out and burn to the ground while fire fighters control spread to adjacent buildings. Part 3 buildings are designed to enable fire fighting from inside and, based on building size and access, include features like sprinklers, improved fire separations, standpipes, fire alarm systems, etc.
 