• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Using OSB on exposed areas?

fosgate3

Registered User
Joined
Aug 2, 2020
Messages
8
Location
Monroe, LA
Hi Building Code Forum. I have a roofing question for you. My mother-in-law's house was recently roofed by a local company. I will try to keep this concise so here goes:

Her house is an early 1950s Craftsman Bungalow style, with exposed overhanging eaves and rafter tails (no soffit). The front porch roof was rebuilt sometime before she had the house and has 1/2" plywood on it while the rest of the house uses 1x6 tongue-and-groove material, typical of the period. A section of the porch roof eave was damaged by a tree and rotten; and had to be replaced.

The house was roofed last week and after inspecting the job, we have a number of concerns. It was all covered by insurance so we haven't signed off on anything yet. One of the main concerns we have is the use of OSB instead of plywood on a large area of the eave of the porch roof. Instead of going back with 1/2" plywood like what was on the rest of the porch roof, the roofing company went back with 1/2 OSB. When I brought it to their attention, the guy told me that the shingle manufacturer, Atlas, recommends OSB on the roofs. I cannot find that information anywhere and I'm waiting for verification from Atlas (I checked on the shingle package and online). What's more is that this is an exposed area and it doesn't make sense to me why this would be considered "okay to do" by the roofers. I thought it was part of IRC/IBC but I'm not finding anything yet so I am coming here to ask the professionals of this forum if using OSB in an exposed area on a roof such as the eave is against building code.

I'd include a picture but haven't yet figured out how to upload one. Maybe that will come with time. Thanks in advance for taking the time to read this. :)
 
Here's a link to a picture of the eave of the roof....I hope this works right. If it does, you will see many of our concerns in this one picture.

1) The issue with the OSB in an exposed area
2) The flashing for the parapet wall is completely wrong and looks hideous.
3) The barge rafter looks like sin (not sure why they did it out of two 2x6s instead of one straight 14' 2x6).
4) That 2x4 "support" block for the barge rafter shouldn't be there.
5) The 10,000 nails sticking through the roof material totally ruins the concept behind the architectural style of the home (and yes, it's like that all the way around the house).

MRgSFQH
 
I asked for my house, and told OSB was fine for decking, because plywood tends to delaminate.

As far as exposed, I cannot answer that question.

As far as exposed nails, kind of nature of the beast.

Give it a few days for better answers
 
= > < =

Here is the image posted by **fosgate3**



2020-08-02-13-44-25.jpg



Q1): What is the applicable Building Code & edition in your area ?
Q2): Did you or the Roofing Contractor obtain a re-roofing permit ?
Q3): Did you sign a contract for the re-roofing ?.................If so,
what does that
contract language state that they will do ?

**fosgate**, ...I looked in the `18 IRC for requirements of the
roof decking materials
and did not see anything specifying the use
of "regular" plywood vs using OSB.......If the spacing of the roof
rafters is 24" o.c., then Table R803.1 requires a roof decking material

to be 5/8" thick.................The application of the "sidewall flashing"
in your photo
appears to be incomplete and incorrect............There
should not be any gap behind the flashing and the framing to
which it is attached.


= < > =
 
The flashing is the only code violation that I see. As to the use of OSB on an overhang...OSB can be used on an overhang if it is rated for the exposure. The shingle manufacturer did not recommend OSB as opposed to plywood. Plywood is a superior product for an overhang both from a maintenance standpoint and aesthetically.

The nails protruding through the sheathing is not a code violation. Short ill-fitting fascia is not a code violation. Both are lousy workmanship and as a consumer I would reject that. Since the job is an insurance repair, the contractor would have to get your permission to use OSB. All of the overhang would be replaced with V-rustic and if I found even one shiner they would do it over again.

Check the contract and see if it says plywood. Whereas the code allows the substitution of OSB for plywood, if a contract or plans specify plywood substitution is not allowed.

Ask your insurance agent to make a site visit and stand your ground.

Place a link to pictures of the fascia, roofing planes and vents (attic and plumbing)
 
Last edited:
The flashing is the only code violation that I see. As to the use of OSB on an overhang...OSB can be used on an overhang if it is rated for the exposure. The shingle manufacturer did not recommend OSB as opposed to plywood. Plywood is a superior product for an overhang both from a maintenance standpoint and aesthetically.

The nails protruding through the sheathing is not a code violation. Short ill-fitting fascia is not a code violation. Both are lousy workmanship and as a consumer I would reject that. Since the job is an insurance repair, the contractor would have to get your permission to use OSB. All of the overhang would be replaced with V-rustic and if I found even one shiner they would do it over again.

Ask your insurance agent to make a site visit and stand your ground.

ICE, this is exactly the information I was looking for. I have long since been told that plywood is superior to OSB for the reasons you just gave. When they delivered the materials, I noticed a sheet of OSB there in spite of the house having no OSB at all. I spoke with one of the people in charge and he first said "well, we have to go back with what's on the roof". When I told him that what's on the roof is 1/2" ply over the porch and 1x6 T&G on the rest, and that there's no OSB anywhere in the house, then he said he would make sure they did ply. I was out of town and came back when the job was done but not before anything was signed off. When I spoke to the same guy again, he made the claim that OSB was recommended, like I described in the original post. I don't like the OSB at all because it will stand out even when painted. It's in two places on the house over the eaves and looks like crap.

Regarding the fascia, we originally told them we didn't want it on there at all. It was not how the house was originally made and was added years later but only in places. We wanted it all taken down and they said they would but then didn't---but then only put new fascia boards up in some places while leaving other places with nothing or old damaged fascia. So either way, it was a bad job done.

You stated the contractor would have to get our permission to use OSB... is there a source I could cite for this? I am going to be meeting with him again this week and I want my ducks in a row (I'm sure he won't just accept the fact that "ICE, the Building Code Forum Moderator" told me so LOL). And regarding the use of V-rustic, is this something they should have to do now since the underside of the eaves of the house is totally <censored>?
 
ICE, this is exactly the information I was looking for. I have long since been told that plywood is superior to OSB for the reasons you just gave. When they delivered the materials, I noticed a sheet of OSB there in spite of the house having no OSB at all. I spoke with one of the people in charge and he first said "well, we have to go back with what's on the roof". When I told him that what's on the roof is 1/2" ply over the porch and 1x6 T&G on the rest, and that there's no OSB anywhere in the house, then he said he would make sure they did ply. I was out of town and came back when the job was done but not before anything was signed off. When I spoke to the same guy again, he made the claim that OSB was recommended, like I described in the original post. I don't like the OSB at all because it will stand out even when painted. It's in two places on the house over the eaves and looks like crap.

Regarding the fascia, we originally told them we didn't want it on there at all. It was not how the house was originally made and was added years later but only in places. We wanted it all taken down and they said they would but then didn't---but then only put new fascia boards up in some places while leaving other places with nothing or old damaged fascia. So either way, it was a bad job done.

You stated the contractor would have to get our permission to use OSB... is there a source I could cite for this? I am going to be meeting with him again this week and I want my ducks in a row (I'm sure he won't just accept the fact that "ICE, the Building Code Forum Moderator" told me so LOL). And regarding the use of V-rustic, is this something they should have to do now since the underside of the eaves of the house is totally <censored>?



Is there a written contract?

If so, any mention of what the decking material will be?


Did they just replace some decking and not the entire deck??? Once again how does the contract read?
 
Is there a written contract?

If so, any mention of what the decking material will be?
Good point. There was a written contract but I don't know if it states anything about the decking material. I will check on that.
 
V-rustic is a personal choice. They should have used 1x6 that matches the rest of the house. At this point they should replace all of the overhang sheathing around the entire house. The wood is splintered and that's the price they pay for being so sloppy.

You should get the insurance company on board prior to meeting the contractor. Because the contractor lied I would fire him. Is there a requirement for a permit?

As to getting your permission to deviate....the contractor doesn't own the house. He can't make decisions for the owner. I get questions from contractors and architects about substantial changes they want to make and I always tell them to get permission in writing from the owner. I suspect that I am unique in that regard.
 
Last edited:
Thank you so very much. I will make arrangements to meet with the insurance adjuster. As for your question about permits, I was told one wasn't needed for re-roofing a house. Now I'm wondering if that's true and I feel a bit foolish for not checking.

Thanks again.
 
As for your question about permits, I was told one wasn't needed for re-roofing a house.
You should call the city permit office, or look on-line, many locations have a list of when permits are required. However, as noted earlier, there aren’t many code violations in the picture, mostly examples of bad work. But if a permit was required but not pulled, that’s one more strike against the contract.
 
I don't mind OSB on vertical surfaces but I mind it on horizontal surfaces. It turns to oatmeal when it gets wet. Another strike against it is that peel and stick membrane does not stick to it very good. I believe the deck collapse in Berkeley a few years back had substituted OSB for ply.
 
Robert ... i think you are confusing osb and mdf when you mention turning to oatmeal when wet. Osb tolerates moisture about as well as ply.

With regard to nails poking through ... doesn’t code require a certain length of nail penetration into the decking, and for 1/2” material i think the nails are required to poke through a little.
 
Plastic cap nail to hold the flashing on the side wall, now that's a new one...beautiful.

I'd check the staple or nailing patterns on the shingles and verify that the vent pipe flashing's are installed properly while your at it with the insurance guy.
 
Unfortunately IRC 905.2.5 requires fasteners to penetrate through the sheathing if the sheathing is less than 3/4" thick.

I agree that the rest of the problems are bad workmanship and not code issues.
 
Thank you so very much. I will make arrangements to meet with the insurance adjuster. As for your question about permits, I was told one wasn't needed for re-roofing a house. Now I'm wondering if that's true and I feel a bit foolish for not checking.

Thanks again.

As usual and in this case, "owner Bewary"
 
If the OSB is rated for exposure, which I have never seen a contractor buy and pretty sure none of our lumber stores carry it in stock. OSB is not an approved exterior siding or finish material unless specifically listed for that type of use. It would be most likely be fine if had a soffit.

The wall flashing is SH!T. Not installed correctly. At minimum should have counter flashing. My biggest concern is that is TRANSITE siding which is an ACBM. Driving nails thru it now makes it damaged and classified as friable and now becomes regulated.

Most contractors don't use superior products. They use the bare minimum the code requires.

As stated already, nails have to penetrate the deck if less than 3/4.
 
You guys that want the nails sticking through are not in California and if you are it's the wrong part of California. There is a short roofing nail made for the overhangs and the nails should not penetrate. It has been done that way for years on millions of roofs with no problems.
 
OSB and plywood swell when wet but plywood pretty much dries to its original thickness and OSB doesn't unless its treated for exposure.
Was there no specifications or standards in the contract? Building codes generally deal with structural and waterproofing issues rather than appearance issues. If you want something to look good you need to describe what you want.
 
and the nails should not penetrate. It has been done that way for years .
Maybe you have been doing it wrong for years. “2015 IBC 1507.2.6 Fasteners. ... a length to penetrate the roofing materials and a minimum of 3/4” into the roof sheathing. Where the sheathing is less than 3/4”, the nails shall penetrate through the sheathing.“

From the Owens Corning installation instructions: All fasteners must penetrate at least 3/4” into the wood deck or completely through the deck by a minimum of 1/4”.
 
I typically see nails through the OSB on new house construction as "e hilton" has posted.

I can't say I see staples coming through. kinda hard to see, they tend to blend in with the OSB.
 
Maybe you have been doing it wrong for years. “2015 IBC 1507.2.6 Fasteners. ... a length to penetrate the roofing materials and a minimum of 3/4” into the roof sheathing. Where the sheathing is less than 3/4”, the nails shall penetrate through the sheathing.“

From the Owens Corning installation instructions: All fasteners must penetrate at least 3/4” into the wood deck or completely through the deck by a minimum of 1/4”.
There's no "maybe" about it.
 