CT still requires incidental storage rooms over 100 SF to be rated 1 hour or automatic fire extinguishing system.
If we are looking at a mixed use F2 and S2 building - non separated how does the incidental storage room requirement come into play.
the s2 use is 900 SF, so its over the 100 sf listed on the incidental use table. and its less than 10%. the F2 area is 9,100 SF. so does it need to be rated per the incidental use table. Or is it not rated because its a mixed use non separated. even if it was separated there is no required separation between F2 and S2.
I guess im trying to figure out whats the difference between storage room as listed on incidental table and a full S2 use.
Opinions greatly appreciated. Thank you!
If we are looking at a mixed use F2 and S2 building - non separated how does the incidental storage room requirement come into play.
the s2 use is 900 SF, so its over the 100 sf listed on the incidental use table. and its less than 10%. the F2 area is 9,100 SF. so does it need to be rated per the incidental use table. Or is it not rated because its a mixed use non separated. even if it was separated there is no required separation between F2 and S2.
I guess im trying to figure out whats the difference between storage room as listed on incidental table and a full S2 use.
Opinions greatly appreciated. Thank you!