I'm doing an addition to an existing building. The addition is a new building attached to the existing building but separated from it by an exit passageway (see attached).
The new building is an A3 occupancy and requires sprinklers.
I guess the general question is whether the sprinkler requirement of one occupancy is extended to the entire building even if the other occupancy does not require sprinklers.

I think based on the section 508.4.1, if the occupancies are separated by a fire barrier than the sprinkler system is not required throughout the building but only required in the occupancy that is required by chapter 9 to have one.
The new building is an A3 occupancy and requires sprinklers.
I guess the general question is whether the sprinkler requirement of one occupancy is extended to the entire building even if the other occupancy does not require sprinklers.

I think based on the section 508.4.1, if the occupancies are separated by a fire barrier than the sprinkler system is not required throughout the building but only required in the occupancy that is required by chapter 9 to have one.