2009 IBC came out with a new use group 422 Ambulatory Health Care Facilities as a subset of B Occupancy. This addition is similarly mirrored in NFPA 101 Chapter 20 Ambulatory Health Care Occupancies.
In putting these facilities in a building with other medical "Outpatient Clinics" (see new definition 304.1.1) NFPA requires a 1-hour rated separation from other building occupants (since it's not B in NFPA), where IBC would not since it's all B - correct me if I'm wrong.
Both codes require that facilities larger than 10,000 sf be separated into smoke compartments. NFPA clearly states sizes are limited to 22,500 sf (20.3.7.3) but IBC's text is silent. However the IBC commentary goes on to state that 10,000 sf is the maximum size of a smoke compartment. Question: Where the IBC code is silent and the commentary conflicts with NFPA's code language - the IBC commentary can be disregarded and is not enforceable, correct? It looks like the State of Washington modified the section to the 22,500 sf when adopting.
The NFPA 20.3.7.2 (3) states: An area in an adjoining occupancy shall be permitted to serve as a smoke compartment for an ambulatory health care facility if the following criteria are met: (a) separating wall and both compartments meet the requirements of 20.3.7. (b) The ambulatory health care facility is less than 22,500 sf. © Access from the ambulatory health care facility to the other occupancy is unrestricted.
This language is not carried over in IBC. If meeting the requirements of NFPA, would the IBC AHJ allow taking refuge in adjoining spaces outside the separated AHCF?
In putting these facilities in a building with other medical "Outpatient Clinics" (see new definition 304.1.1) NFPA requires a 1-hour rated separation from other building occupants (since it's not B in NFPA), where IBC would not since it's all B - correct me if I'm wrong.
Both codes require that facilities larger than 10,000 sf be separated into smoke compartments. NFPA clearly states sizes are limited to 22,500 sf (20.3.7.3) but IBC's text is silent. However the IBC commentary goes on to state that 10,000 sf is the maximum size of a smoke compartment. Question: Where the IBC code is silent and the commentary conflicts with NFPA's code language - the IBC commentary can be disregarded and is not enforceable, correct? It looks like the State of Washington modified the section to the 22,500 sf when adopting.
The NFPA 20.3.7.2 (3) states: An area in an adjoining occupancy shall be permitted to serve as a smoke compartment for an ambulatory health care facility if the following criteria are met: (a) separating wall and both compartments meet the requirements of 20.3.7. (b) The ambulatory health care facility is less than 22,500 sf. © Access from the ambulatory health care facility to the other occupancy is unrestricted.
This language is not carried over in IBC. If meeting the requirements of NFPA, would the IBC AHJ allow taking refuge in adjoining spaces outside the separated AHCF?