• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Pneumatic pipe bursting

Pcinspector1 said:
Is pneumatic pipe bursting addressed by the I-codes?pc1
A little more detail about your question? Pneumatic as in controls or are you referencing air lines as in work stations for garages and assembly plants?
 
Please see Wikipedia definitions: Pipe Bursting.

Pipe bursting is a trenchless method of replacing buried pipelines.

pc1
 
Pcinspector1 said:
Please see Wikipedia definitions: Pipe Bursting. Pipe bursting is a trenchless method of replacing buried pipelines.

pc1
Never heard it called that. Folks around here call it sewer lining, or pipe lining. I've also only seen it done to municipal lines.

Not addressed in the I-codes to the best of my knowledge.

mj
 
mjesse said:
Never heard it called that. Folks around here call it sewer lining, or pipe lining. I've also only seen it done to municipal lines.Not addressed in the I-codes to the best of my knowledge.

mj
That is what I have referred to it as.
 
mjesse said:
Never heard it called that. Folks around here call it sewer lining, or pipe lining. I've also only seen it done to municipal lines.Not addressed in the I-codes to the best of my knowledge.

mj
Same scenario here in South Carolina - Pipe lining is what it is referred to and according to our state laws, the I-codes wouldn't regulate it as it is a public utility company doing the work.
 
I see it a lot. The procedure is as follows:

Run a camera in my presence before starting the work to ascertain that there are no major offsets or branch lines that will be cut off from the building sewer.

Install the pipe by pulling a breaker head and the pipe through the existing pipe.

Fill it with water. Then release the water and run the camera in my presence to ascertain that there are no low spots holding water and that fusion joints have been reamed.

There is another trench-less sewer method that involves an inverted sock that is installed with compressed air. It is a liner and we do not allow it as it is a patch and not a pipe.
 
Wanted to bring this one back up for discussion. We have had a contractor in town doing pipe bursting (got started, and almost finished before we had a chance to review or even know what material he was using) and now we have someone requesting approval for pipe lining, on the sewer line from main to house.

Has anyone found documentation to allow, or cause to disallow, either method?
 
We allow the material and method. Before the work starts a camera run is required to determine if there are any lines that will be cut off or major offsets that make the method inappropriate. After the job is completed another camera run is done. This time the pipe should be full of water. The weenie is pulled and the water drained. Now you are looking for low spots that collect water. The other thing to look for is fused joints. There is a tool that will ream the pipe where it has been fused together. If that isn't done, there will be a ridge that can trap solids.
 
Last edited by a moderator:
& : & : &



Darren,

Before the Contractor in your town started on the "bursting project",

...were there any specifications \ standards \ etc. submitted for review

& approval by the AHJ ?



& : & : &
 
We have allowed trenchless or (pipe bursting) for years. It is less intrusive to the landscaping. The material a High Density Polyethylene with a life time of 50+ years they tell me.
 
Darren Emery said:
ICE - are you referring to bursting, or lining?
Bursting where a new pipe is pulled. The liner type has the same camera runs but there is no fused joint to ream.
 
north star said:
& : & : &

Darren,

Before the Contractor in your town started on the "bursting project",

...were there any specifications \ standards \ etc. submitted for review

& approval by the AHJ ?



& : & : &
No - they just called for a sewer repair/replacement permit, and then we found out what they were doing at time of inspection.
 
& : = : &





It may be time to "throw the brakes on" the whole project,

until some more thorough criteria \ standards can be researched,

and verified..........Just sayin'



& : = : &
 