• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

exit discharge

  1. Harrison Staab

    Exit Discharge from Interior Exit Stair Remoteness or Separation Distance Requirement?

    For a 5 story (not a high rise) Type III Group R-2 Apartment building fully sprinklered per NFPA 13 in sunny California (CBC 2019): Project has two Interior Exit Stairways connected by a 1-hr corridor exceeding the separation requirement of 1007.1.1 (>1/3 building diagonal per exception 2). Due...
  2. S

    Interior exit stairway and ramp separated from exit passageway by a horizontal assembly

    2015 1023.3.1 Extension. Where interior exit stairways and ramps are extended to an exit discharge or a public way by an exit passageway, the interior exit stairway and ramp shall be separated from the exit passageway by a fire barrier constructed in accordance with Section 707 or a horizontal...
  3. eyan50495

    Exit Discharge on Public Way

    A question came up today at my office about discharging a stair. This is NYS IBC and is a multifamily building. We are trying to determine if your stair can exit onto a public way. We are trying to determine what the code says not necessarily what is good practice. There is a road on our...
  4. C

    Exit Discharge

    I've designed an apartment building that has been separated into two buildings by a 2 hr. firewall. This will be used as a horizontal exit for occupants exiting from the left building to the right building. The code official reviewing plans is siting section IBC 2018 1022.1 regarding exit...
  5. C

    Elevated Buildings in flood zone and exit access and exit discharge

    First post - wanted to make a good one. I am trying to interpret a few things mainly including "Building" and "exit discharge". Quick code items = type II-B, full concrete construction, fully sprinklered, Business occupancy, 462 total occupants, 24,217 total SF (1st & 2nd floors), V-22 flood...
  6. R

    Exit Access Stair in Open Parking Garage - Exit Discharge

    Hello all, I'm working on a project that includes a 6 story open parking garage which is non-sprinklered. After my code research, I cannot find a definitive determination if I can have a stair that does not egress directly to the outside of the building. Per IBC 2018 section 1019.3, condition...
  7. M

    Discharge through a fire truck parking shed

    I'm working on a fire station plan that needs two exits one of those exits is discharge directly to an adjacent fire truck parking shed, I need to know can I consider this an exit discharge what part of the code that discuss my case? According to "IBC 2015" 1028.1 General. Exits shall...
  8. J

    Egress Court Question

    We are having a dispute with a building reviewer regarding an Egress Court (2015 IBC Section 1028.4.2). We have two stairs that exit our building (5-story R-2 over 2-story S-2 garage) on the same side of our property. The stairs are inset and exit 10'-8" away from the property line. The...
  9. S

    903.2.1.2 Group A-2 & 2nd floor

    The fire area with 2nd story exit terminates at the point of exit discharge, thus the 2nd floor fire area is located on a floor with the same level of exit discharge serving the 1st floor level of exit discharge. OR; Is this what the confusing IBC code actually means?: All new buildings (say...