• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

1" tolerance at sink?

Yikes

Gold Member
Joined
Nov 2, 2009
Messages
3,064
Location
Southern California
I just read a CASp report done by a very respected inspector for a very large transit center. In the restrooms, there is a sink with CL 17" away from the end wall. CBC 11B-606.6 requires a minimum of 18".

The CASp report says:
  • "The centerline of the lavatory is 17" from the adjacent wall (minimum 18" required). We believe this is within 'dimensional tolerance' and no action is recommended".
Since when is a "minimum" dimension allowed to have ANY tolerance?
 
Even minimum and maximum dimensions have construction tolerances. However, with that stated, 1 inch is a rather large tolerance for a sink location in my opinion--I would say that a +/- 1/4-inch tolerance is more realistic and achievable.
 
I agree with Ron
Where a requirement is a minimum or a maximum dimension that does not have two specific minimum and maximum end points, tolerances may apply. but, 1"is excessive.
The restroom may have been designed for no tile and changed to tile.
 
And in the real world, that 1" will never ever make any difference to anyone who ever uses that sink.

I'd have written it up just like he did.
 
  • Like
Reactions: ICE
And in the real world, that 1" will never ever make any difference to anyone who ever uses that sink.

I'd have written it up just like he did.
While I agree that 1" is trifling with regards to the placement of a sink the fact that this is California Accessibility 1" is as good as a mile. Recently I caused the lowering of a urinal 1"....of course with that one I had a vision of pee on my boots and thought ....You know......
 
We saw this coming with regards to CASps.
In court this may be seen as a "technical" violation of the CBC but has it damaged the plaintiff? That remains to be proven.
As to tolerance, see the recent 9th Circuit appeal findings with regards to City of San Francisco specific to tolerances. Bill Hecker is the defense expert.
 
We saw this coming with regards to CASps.
In court this may be seen as a "technical" violation of the CBC but has it damaged the plaintiff? That remains to be proven.
As to tolerance, see the recent 9th Circuit appeal findings with regards to City of San Francisco specific to tolerances. Bill Hecker is the defense expert.
ADAguy, do you have a link or a court case citation?
 
Note that ICC A117.1 Standard for Accessible and Usable Buildings and Facilities started moving away (in the 2003 edition) from indicating "fixed" values for many dimensions. The fixed dimensions relied on inspection to consider what is "reasonable construction tolerances" . No one can build to a fixed dimension and be "on the mark" every time. The classic example is the well known "18 inches from the center of a WC to the wall" for an accessible toilet. Now, ICC A117.1 indicates a dimension range of 16 to 18 inches. Therefore, if you shoot for 17 inches, there is a high probability that you end up (at inspection) being in the range of 16-18 inches. The key is to NEVER design to a maximum or a minimum because doing so causes the actual dimension to (sometimes) exceed those values.
 
You would never get a 1" tolerance on that application. Cannot understand how a licensed CASp would allow that.
 
so maybe this CAsp is thinking, if toilets used to be exactly 18" and now they're 16-18", that's the code self-confessing that 1" tolerance is really OK??
 
Case was an interesting read. No, I wouldn't think because 1 inch tolerance allowed for one thing that same tolerance works for other dimensions.
 
In California, sinks adjacent to a side wall or other obstruction require 18" minimum clearance. This exceeds ADA, but we also have the Unruh civil rights act, so I don't want the client getting sued under state law for a building code-related accessibility violation.
 
No, it's not an alcove. The 18" to CL is triggered by a unique section in California code:

11B-606.6 Adjacent side wall or partition. Lavatories, when
located adjacent to a side wall or partition, shall be a minimum
of 18 inches (457 mm) to the centerline of the fixture.
 