• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2009 IECC Metal Building

Jeff W

Member
Joined
Nov 6, 2013
Messages
9
Location
Missouri
I am running COMcheck on a prefab metal building. The building is in the 2009 IECC. We are using rolls of R19 on the roof and Walls. Can I consider this continuous since the batts run over the purlins? We are also using Thermal blocks on the roof but COMcheck for 2009 IECC doesn't take this into consideration.

Jeff
 
No, I would not consider it continuous since the thermal blocks are most likely only R-5. COMcheck may not be appropriate for a pre-engineered metal building? You may want to look at the 2009 IECC Table 502.1.2 for Metal Buildings.
 