• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2009 IRC Rebar in Footings

Status
Not open for further replies.

Durant

Bronze Member
Joined
Aug 6, 2012
Messages
86
Location
Oklahoma
Most cities in Oklahoma the inspectors are requiring four #4 horizontal rebars in the footing, or two #5 stacked. I find that no rebar is required in the 2009 IRC except that foundation with stemwall one 12 inches from top of stemwall and one within 3 or 4 inches of bottom of footing (R403.1.3.1).

No siesmic requirements here. According to 2009 code I don't find where any rebar is required in the footing accept where a stemwall is added.

Is rebar required in footings and am I missing something?
 