2009 IBC - New Jersey Edition
Type VB
Three Stories
R-2 Use w/ S-2 private garages on one side of bldg. at grade
No basement
Fully sprinklered
10 units per building/fire area (2 + 4 + 4)
Ground floor: 2 units one side of bldg, 6 individual private garages on other side. 2 means of egress provided from corridor to exterior.
2nd and 3rd floors: 4 units/floor. Units exit to corridor and to one exit stair as per sections 1021, 1022 and table 1021.2
Questions:
1. Does the exit stair on floors 2,3 need to be an exit enclosure or can the stair be open?
2. If a fire barrier (2 hour) is provided, can modules of 10 units be attached to create a 20 and 30 unit building? Each fire area will have 4 units/story per exit.
Thank you,
Scott
Type VB
Three Stories
R-2 Use w/ S-2 private garages on one side of bldg. at grade
No basement
Fully sprinklered
10 units per building/fire area (2 + 4 + 4)
Ground floor: 2 units one side of bldg, 6 individual private garages on other side. 2 means of egress provided from corridor to exterior.
2nd and 3rd floors: 4 units/floor. Units exit to corridor and to one exit stair as per sections 1021, 1022 and table 1021.2
Questions:
1. Does the exit stair on floors 2,3 need to be an exit enclosure or can the stair be open?
2. If a fire barrier (2 hour) is provided, can modules of 10 units be attached to create a 20 and 30 unit building? Each fire area will have 4 units/story per exit.
Thank you,
Scott