• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2015 Fireplace Walls

Francis Vineyard

Registered User
Joined
Jan 1, 2010
Messages
3,105
Location
Charlottesville, VA
In the 2015 IECC and IRC is an air barrier still required to be installed on fireplace walls?

2009 IECC Table 402.4.2 and IRC Table N1102.4.2; Fireplace walls include an air barrier.

2012 IECC; Table 402.4.1.1 and IRC Table N1102.4.1.1; An air barrier shall be installed on fireplace walls. Fireplaces shall have gasketed doors.
 
RE86-13 removed that portion of the table.
Proponents reason statement includes "In 2012 Table R402.4.1.1 Fireplace criteria states an air barrier shall be installed on fireplace walls. Fireplaces shall have gasketed doors. In Section R402.4.2 it states new wood-burning fireplaces shall have tight-fitting flue dampers or doors, and outdoor combustion air. We interpret this to mean traditional, field-fabricated, “masonry fireplaces” in accordance with 2009 IRC Section R1001, and constructed of concrete or solid clay-masonry units; NOT “factory-built,” UL 127 fireplaces in accordance with IRC Section R1004. Because of requirements in the IECC that require all fireplaces to be provided with gasketed doors, a great deal of controversy has resulted. Most factory-built fireplaces are not tested for use with sealed glass doors and installing such doors on fireplaces that are not tested for these doors could cause overheating of the fireplace resulting in a fire hazard. Without testing, the effect of the doors will be an unknown. In this regard, the intent of Section R402.4.2 is to mitigate air leakage during periods of non-use, but not where the conditions of fireplace installation are in violation of the UL 127 listing. This will address chase seal details that are needed and gives clarification to address framed wall construction.
Please note that deleting the air barrier requirement for fireplace walls has not (sic) net effect as there are at least 2 other locations in the table where the air barrier requirement for walls is restated and such would include fireplace walls."
 
[QUOTE="there are at least 2 other locations in the table where the air barrier requirement for walls is restated and such would include fireplace walls."[/QUOTE]

Not clear to me the other locations? Item 1 in the table seems to be about the exterior side, what is the other location?
 
Proponent: Thomas Stroud, Senior Manager, Codes & Standards, representing Hearth, Patio & Barbecue Association (stroud@hpba.org)
Also included in the proposal was to include fireplace chases to the "Shafts, penetrations" portion of the table. This change didn't make it into the final version. perhaps this is an errata(?). The committee amended part of the proposal, but not the table.
http://www.iccsafe.org/wp-content/uploads/04A-IECC-R.pdf page 152.
 
I know. I checked before posting. That doesn't mean that there isn't an errata, just not yet reported and acknowledged.
 