• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2015 IRC 302.2 membrane penetration

jmartinarch

Registered User
Joined
Apr 18, 2017
Messages
2
Location
Washington
Per this section the common wall shall be constructed without plumbing or mechanical equipment, ducts or vents in the cavity of the common wall.
I have a double wall. 2x4's with 5/8" type x each side, an airspace. Structure requires that a beam penetrate one layer of GWB and sits on multiple 2x4's. The beam is wrapped with 5/8" GWB. The beam is not continuous through to the next townhouse.
The plan reviewer states that the beam penetrates the one-hour separation wall. Either the support posts should be located outside the wall or provide a method of protecting the beam penetration.

Does this sound reasonable? If so, what is an acceptable method of protecting the beam penetration.
And, since the code does not mention that beams or other structure cannot penetrate the one-hour wall, should this even be an issue?

Thanks,
JM
 
Agree penetration allowed

Some others can give better commentary


Did the plan reviewer cite that section???


Does this answer your question



R302.2.4 Structural independence.
Each individual townhouse shall be structurally independent.

Exceptions:

1. Foundations supporting exterior walls or common walls.

2. Structural roof and wall sheathing from each unit fastened to the common wall framing.

3. Nonstructural wall and roof coverings.

4. Flashing at termination of roof covering over common wall.

5. Townhouses separated by a common wall as provided in Section R302.2, Item 1 or 2.
 
See R302.4.2 in the 2012 IRC for membrane penetrations. R302.4.1.1 requires that penetrations be installed as tested in the approved fire-resistance rated assembly.
 
Sorry I read the question wrong, I thought it was penetrating to another unit.

""Structure requires that a beam penetrate one layer of GWB and sits on multiple 2x4's. The beam is wrapped with 5/8" GWB. The beam is not continuous through to the next townhouse.""


Not sure why the plan reviewer has a problem with this set up??
 