redbird11
The 2018 IBC defines a corridor as: An enclosed exit access component that defines and provides a path of egress travel. IMC does not contain a definition.
My project is not required to have rated corridors. However, IMC 601.2 says -
Corridors shall not serve as supply, return, exhaust, relief or ventilation air ducts.
So if I don't call them corridors and call them hallways or "unrated corridors" can I use them for return air?
- Use of a corridor as a source of makeup air for exhaust systems in rooms that open directly onto such corridors, including toilet rooms, bathrooms, dressing rooms, smoking lounges and janitor closets, shall be permitted, provided that each such corridor is directly supplied with outdoor air at a rate greater than the rate of makeup air taken from the corridor.
- Where located within a dwelling unit, the use of corridors for conveying return air shall not be prohibited.
- Where located within tenant spaces of 1,000 square feet (93 m2) or less in area, use of corridors for conveying return air is permitted.
- Incidental air movement from pressurized rooms within health care facilities, provided that the corridor is not the primary source of supply or return to the room.