• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2019 CPC-422.2 OL Factor

Mr209Smith

Registered User
Joined
Feb 21, 2018
Messages
21
Location
California
Good Afternoon!

I am a Plans Examiner for an AHJ in California and we are having an internal debate regarding 2019 CPC 422.2 Separate Facilities, 2019 CPC Table 4-1, and the 2019 CBC Chapter 10. Your input would be greatly appreciated.

Exception 3, in business and mercantile occupancies with a total occupant load of 50 or less, only one restroom is required. Do you calculate the total occupant load using the OL factor from Table 4-1, or do you use the OL factor from Chapter 10 of the CBC, when determining if the occupancy requires two restrooms?

Thank you!
Philip
 