• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

30 occupant Group A, B & F on 2nd floor - single exit

sergoodo

Registered User
Joined
Oct 27, 2009
Messages
298
Non Sprinkled Building
Does the A Group with 30 occupants require <100' egress?


EGRESS TRAVEL DISTANCE
0’<exit access...exit access stair>75’<exit><exit level of discharge>75’
0’< 2nd floor > < 1st Floor > 75’
Table 1006.2.1
Non Sprinklered <30 Occupants
EGRESS <75’ Groups A&F
EGRESS <100’ Groups B & Group A (<50occ load)
1006.3.2 Single exits.
A single exit or access to a single exit shall be permitted from any story or occupied roof where one of the following conditions exists:
2.Rooms, areas and spaces complying with Section 1006.2.1 with exits that discharge directly to the exterior at the level of exit discharge, are permitted to have one exit or access to a single exit.
 
ok back step

If you have 30 or less, in what looks like a Group A,,,

You might not be a Group A????

B??
 
If you’re less than 50 occupants, it is not a Group A, but probably a Group B. For a single exit from a second story Group B, the occupant load is limited to 29–above 29 (i.e., 30) requires two exits.
 
If you’re less than 50 occupants, it is not a Group A, but probably a Group B. For a single exit from a second story Group B, the occupant load is limited to 29–above 29 (i.e., 30) requires two exits.
RLGA, please tell me the reference of this further limitation down to 29 occupants. After the CPET >75 feet the 2nd exit is required > 29 occupants?

Or 2015 IBC Table 1006.2.1 has Group B limit at 49 occupants for single 2nd floor exit requirement modified elsewhere?
 
RLGA, please tell me the reference of this further limitation down to 29 occupants. After the CPET >75 feet the 2nd exit is required > 29 occupants?

Or 2015 IBC Table 1006.2.1 has Group B limit at 49 occupants for single 2nd floor exit requirement modified elsewhere?
Table 1006.3.2(2) per Section 1006.3.2, Condition 1. Condition 2 permits only rooms and spaces to have a single exit to the exterior if they are on the level of exit discharge; if on the second story, going down stairs is not considered to be discharging at the level of exit discharge.
 
Table 1006.3.2(2) per Section 1006.3.2, Condition 1. Condition 2 permits only rooms and spaces to have a single exit to the exterior if they are on the level of exit discharge; if on the second story, going down stairs is not considered to be discharging at the level of exit discharge.

Bang harder, I disagree. "Table 1006.2.1 is for “spaces” only—not stories." is the best place to bang.

1006.3.2(2) STORIES WITH ONE EXIT OR ACCESS TO ONE EXIT FOR OTHER OCCUPANCIES
Clarify how to determine which table appropriate to use...they conflict.

THIS is the conflict
  1. You can have 49 people on the 2nd story in a Group B room with access to only one (1) of the two (2) exits BUT the one (1) exit CPET must be <75’ that discharge directly to the exterior at the level of exit discharge.
  2. You cannot have 49 people on the 2nd story in a Group B building with access to only one (1) exit with CPET <75’ that discharge directly to the exterior at the level of exit discharge.




CPET<75’ single exit is permitted from any story with an exit that discharges directly to exterior..If you are in a second floor room open the door directly to the stairwell, you are still in the exit access portion and have not reached the exit discharge. The door at the bottom of the stairs is another exit access doorway; and if terminates/discharges to the exterior/public way; and you have traveled less than 75’: The IBC says complies with the absolute minimum safety requirements.


1006.2.3 says “any story”, IBC would have clarified with “located on a floor other than a level of exit discharge”, as it did so in the sprinkler posting.



IBC 2015
1006.3.2 Single exits.
A single exit or access to a single exit shall be permitted from any story or occupied roof where one of the following conditions exists:
2. Rooms, areas and spaces complying with Section 1006.2.1 with exits that discharge directly to the exterior at the level of exit discharge, are permitted to have one exit or access to a single exit.


EXIT ACCESS. That portion of a means of egress system that leads from any occupied portion of a building or structure to an exit.
EXIT ACCESS STAIRWAY. A stairway with the exit access portion of the means of egress system.
EXIT. That portion of a means of egress system between the exit access and the exit discharge or public way. Exit components include exterior exit doors at the level of exit discharge, interior exit stairways and ramps, exit passageways, exterior exit stairways and ramps and horizontal exits.
EXIT DISCHARGE. That portion of a means of egress system between the termination of an exit and a public way.
LEVEL OF EXIT DISCHARGE. The story at the point at which an exit terminates and an exit discharge begins.




 
Last edited:
I disagree. By your logic, I could have a Group B sprinklered building of multiple stories (3 plus) with only one stairway as long as the exit discharges directly to the exterior at the level of exit discharge (nearly all exit stairs must, so nothing unique there), the occupant load does not exceed 49, and the CPET does not exceed 100 ft. That is not the intent—you’re reading more into the condition than what was intended. Condition 2 does not apply to stories. Period.

You can try it, but I doubt it will make it through the first plan review without pushback from the B.O. I personally would not approve it and, as an architect, I would not put my seal on it.
 
I disagree. By your logic,

Not my logic. The logic of 1006.3.2 stating 'single exit shall be permitted from any story'. I agree, not understood, requires a clarification or correction.

Nothing to try, just processing TPS reports: 1006.3.2 reports coming back not possible for single exit rooms or spaces to use maximum occupancy loads on 'Table 1006.2.1' for any other story than the ground floor level of exit discharge.
 
2018 IBC don't have a 2015
1006.1 General.
The number of exits or exit access doorways required within the means of egress system shall comply with the provisions of Section 1006.2 for spaces, including mezzanines, and Section 1006.3 for stories or occupied roofs.

You cannot use 1006.2 for a story above grade plane
 
Diagram of 2 rooms with 30 occ of the building's 2nd floor with 2 exits directly to exterior

< EXIT 30occ [partition] 30occ EXIT >

I say each room requires 2 exits or is this the 1006.3.2 logic if <75' exit access to the discharge?
 
Diagram of 2 rooms with 30 occ of the building's 2nd floor with 2 exits directly to exterior

< EXIT 30occ [partition] 30occ EXIT >

I say each room requires 2 exits or is this the 1006.3.2 logic if <75' exit access to the discharge?
I agree; every occupant on the second story must have access to two exits. The story, as a whole, is considered when applying Table 1006.3.2(2).
 
Top