1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

30A Breaker on 14awg wire. Legal?

Discussion in 'Electrical Codes' started by jar546, Nov 7, 2018 at 7:17 PM.

Tags:
  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,656
    Likes Received:
    244
    I just ran conduit for a 2 HP 230V single phase motor using 14awg THHN wire protected by a 30A InvTime breaker. Are there any code issues with this installation?
     
  2. TheCommish

    TheCommish Sawhorse

    Joined:
    Sep 27, 2011
    Messages:
    721
    Likes Received:
    54
    just the impending melting wire and fire
     
    JBI likes this.
  3. chris kennedy

    chris kennedy Sawhorse

    Joined:
    Oct 24, 2009
    Messages:
    1,297
    Likes Received:
    66
    No NEC at my desk here but at first glance that motor likely has internal OL protection so your golden.
     
    jar546 likes this.
  4. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    5,656
    Likes Received:
    244
    You are correct. This is one of those situations that are perfectly code compliant.
     