2 story building, mixed use, first floor Mercantile or Business, second floor R-2 (3 One bedroom apartments). Each floor 2400 sf., non sprinklered, 2 Hour floor separation, 2012 I Codes
table 1004.1.2 R occupant load 200 Gross yields 12 occupants on second floor, table 1015.1 says R over 10 requires 2 exits,
1007.1 "Where more than one means of egress are required by Section 1015.1 or 1021.1 from any accessible space, each accessible portion of the space shall be served by not less than twp accessible means of egress"
1007.3 Stairways - 48" and area of refuge.
does this seem correct.