• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Accessory space

I don't have any one S-1 over 12,000 sq ft and the total of all S-1 does not exceed 24,000 sq ft.
Well, yes, you do. To be considered a fire area separating a Group S-1 occupancy from a Group B occupancy or between Group S-1 occupancies, the fire-resistance rating for the fire barrier must be 3 hours per IBC Table 707.3.10. Any openings must also be 3 hours per IBC Table 716.1(2).
 
Well, yes, you do. To be considered a fire area separating a Group S-1 occupancy from a Group B occupancy or between Group S-1 occupancies, the fire-resistance rating for the fire barrier must be 3 hours per IBC Table 707.3.10. Any openings must also be 3 hours per IBC Table 716.1(2).
So, if I don't have any 3 hour walls separating the S-1 from other areas, it's basically all S-1 and 24,000 sq ft is the limit without sprinkler.
 
Well, yes, you do. To be considered a fire area separating a Group S-1 occupancy from a Group B occupancy or between Group S-1 occupancies, the fire-resistance rating for the fire barrier must be 3 hours per IBC Table 707.3.10. Any openings must also be 3 hours per IBC Table 716.1(2).

So, if I don't have any 3 hour walls separating the S-1 from other areas, it's basically all S-1 and 24,000 sq ft is the limit without sprinkler.

Correct (kind of). As it is all interconnected, and being that you have no 3-hr fire barriers, you have a single fire area that is well over 12,000sf. NFPA 13 system should be required. It is not all S-1, but the fire area would be inclusive of both the B and S-1.
 