1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Adjusting Lintel Height

Discussion in 'Residential Foundation Codes' started by jar546, Jun 20, 2013.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,697
    Likes Received:
    722
    These are exterior walls but I am thinking this is a more appropriate area to post since it is CMU construction.If you look at the photo you will see that the garage lintel is shimmed up approximately 2" for purposed of making the required R.O.As a result, the block directly above the lintel had to be cut down 2" so it would match up with the rest of the block for the bond beam pour.The issue is that the lintel assembly was specified on the drawings as 32" which is now 30", therefore the construction is not per approved plans. The good news is that this particular lintel is for the only gable on the house and weight is not an issue so the RDP had no problem firing off a letter stating so. There are several other homes with this design that are going to be built and I have thought of 2 fixes. Let me know if you can think of any more:1) Change the prints to show a 30" lintel assembly.2) Change the slope of the garage floor from 1/8" pitch to approximately 1/4" pitch to drop the opening another 2" and we no longer have to look at the cluster around the lintel with the cut and notched block.What say thee?Home built to 170mph wind

    View attachment 1814

    View attachment 1814

    /monthly_2013_06/p1803075264-5.jpg.96901e03e63067a9f12e478275c40d73.jpg
     
  2. globe trekker

    globe trekker Registered User

    Joined:
    Oct 19, 2009
    Messages:
    1,739
    Likes Received:
    0
    3) Have them install the correct sized lintel as per the designed plans.

    .
     
  3. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,697
    Likes Received:
    722
    The size of the lintel is correct. The thickness for the pouring of the bond beam is wrong
     
  4. GBrackins

    GBrackins Registered User

    Joined:
    Nov 11, 2009
    Messages:
    454
    Likes Received:
    0
    I'd recommend changing the lintel to 30" if it meets the design calculations for load and approved by the RDP. a 1/4" per foot slope can be detectable as sloped floor, whereas a 1/8" usually isn't notice.
     
  5. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,956
    Likes Received:
    661
    "1) Change the prints to show a 30" lintel assembly."

    Change the prints to show a 30" minimum lintel assembly.

    Or minimum XXX
     
  6. cboboggs

    cboboggs Moderator

    Joined:
    Oct 19, 2009
    Messages:
    280
    Likes Received:
    0
    Change the prints.
     
  7. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    If this was a sealed drawing you can't change the prints. Only the DP can do that!
     
  8. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,956
    Likes Received:
    661
    That's what I assumed we were talking about, have the DP do an addenda, or a new page with the alteration.
     
  9. peach

    peach Registered User

    Joined:
    Oct 17, 2009
    Messages:
    2,834
    Likes Received:
    2
    why 170 mph? That's just a little overkill, but the RDP probably won't change it if that's the required wind speed/pressure is.
     
  10. Rio

    Rio Silver Member

    Joined:
    Mar 31, 2010
    Messages:
    224
    Likes Received:
    0
    It's awfully difficult to get a concrete floor to drain when the pitch is 1/8:12................ Be a good idea to make it 1/4:12 although as pointed out the slope is noticeable.
     
  11. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    7,224
    Likes Received:
    1,084
    Hire real masons that layout their block to hit the heights required........We always ordered welded steel door jambs with a head that lined up with typical coursing....adjustments can be made starting at the bottom....
     
  12. RJJ

    RJJ Platinum Member

    Joined:
    Oct 17, 2009
    Messages:
    2,940
    Likes Received:
    60
    Fatboy: Yes and those of us that understand would assume that the DP make the change. However, someone with little experience may take it on themselves to just make the change / red line the drawing. Limited experience may assume he/she can do such a thing.
     
  13. globe trekker

    globe trekker Registered User

    Joined:
    Oct 19, 2009
    Messages:
    1,739
    Likes Received:
    0
    Unfortunately "steveray", there are not that many real masons left, and the good ones are

    far & few in between. Also, a real mason would probably not be cost effective to hire,

    when a contractor can hire almost anyone to install sloppy work, ..not read any plans,

    ..blame the inspector for any and all faults on the project, and have the AHJ to allow it

    because of politics. Just read some of the posts on this Forum from "Sifu", .."codeworks",

    "Alias" and others.

    They can and DO regularly in some areas of the country!

    .
     
    #13 globe trekker, Jun 21, 2013
    Last edited by a moderator: Jun 21, 2013
  14. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    7,697
    Likes Received:
    722
    On the center column of block, that would have been possible. On the ends, they terminate in corners that are set up for the rest of the elevations so that was not an option.
     
  15. Keystone

    Keystone Registered User

    Joined:
    Feb 23, 2010
    Messages:
    1,022
    Likes Received:
    137
    Have RDP spec bond beam, flexibility to place additional bar or adjust current sizing
     