texasinspector
Where in the IBC can I locate the minimum clearance to grade for a brick veneer exterior wall on a slab-on-ground foundation?
Thanks,
Thanks,
Tied to the studs with wall ties. Not adhered.Is the brick adhered veneer or anchored veneer? i.e. is it stuck to the exterior wall or is it self-supporting and tied to the exterior framed wall?
Thanks!Building Code of the Texas IHB (2015 IBC) [BS] 1405.10.1.3 Clearances
On exterior stud walls, adhered masonry veneer shall be installed not less than 4 inches (102 mm) above the earth, or not less than 2 inches (51 mm) above paved areas, or not less than 1/2 inch (12.7 mm) above exterior walking surfaces that are supported by the same foundation that supports the exterior wall.
Well, that was premature. that citation applies only to adhered. This is brick veneer that is anchored with wall ties to the studs.Thanks!
I think you need to go to TMS 402/ACI 530/ASCE 5Well, that was premature. that citation applies only to adhered. This is brick veneer that is anchored with wall ties to the studs.
Thx2015 IBC 1405.4.2 indicates there may be courses of masonry that are not above finished ground level, since it requires the weeps to be in the first course above finished ground level.
ThxI think you need to go to TMS 402/ACI 530/ASCE 5
Building Code of the Texas IHB (2015 IBC)[BS] 1405.6 Anchored Masonry Veneer
Anchored masonry veneer shall comply with the provisions of Sections 1405.6, 1405.7, 1405.8 and 1405.9 and Sections 12.1 and 12.2 of TMS 402/ACI 530/ASCE 5.