• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Are sprinklers required for an outdoor assembly area under a metal canopy?

Nearly-Complete

Registered User
Joined
Feb 8, 2019
Messages
27
Location
California
If this was enclosed, sprinklers are clearly required: A-2 occupancy with occupant load factor of 15, 1750 square feet, so occupant load of 117 which requires sprinklers per 903.2.1.2.

The architect thinks this does not meet the definition of a fire area. The fire chief does.

I’m in California but it looks like this is model code language:

Ch 2 Definitions:
Building: Any structure used or intended for supporting or sheltering any use or occupancy.

Fire Area: The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls, OR horizontal assemblies of a building. Areas of a building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
 