2012 IBC. Non-sprinklered existing building.
Scenerio: A building contains 2 occupancies (proposed to be non-separated uses), A-2 and B. The building area is 6000 spuare feet, meeting area and height of section 503.
The A-2 occupancy has an occupant load of 85, the neighboring B load is 20 (these numbers are only for example).
The A-2 area is, say, 4000 square feet.
There is only a 1 hour fire barrier between the two uses.
The entire building exceeds the 5000 foot fire area threshold for sprinklers (903) for an A-2.
The occupanct load is 85 for the A-2, but if one adds the 20 from next door (due to no 2 hr separation), this puts the overall load at 105.
Conclusion: Either the building needs to be sprinklered, or 2 hour fire barrier installed due to both the area issue and the occupant load issue.
Correct? and Thank you all in advance and... Happy Thanksgiving.
Scenerio: A building contains 2 occupancies (proposed to be non-separated uses), A-2 and B. The building area is 6000 spuare feet, meeting area and height of section 503.
The A-2 occupancy has an occupant load of 85, the neighboring B load is 20 (these numbers are only for example).
The A-2 area is, say, 4000 square feet.
There is only a 1 hour fire barrier between the two uses.
The entire building exceeds the 5000 foot fire area threshold for sprinklers (903) for an A-2.
The occupanct load is 85 for the A-2, but if one adds the 20 from next door (due to no 2 hr separation), this puts the overall load at 105.
Conclusion: Either the building needs to be sprinklered, or 2 hour fire barrier installed due to both the area issue and the occupant load issue.
Correct? and Thank you all in advance and... Happy Thanksgiving.