• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

at the last minute

ICE

Oh Well
Joined
Jun 23, 2011
Messages
12,856
Location
California
At the first inspection, I wrote a correction that the service drop is too close to the water. That old style drop must be changed to a triplex and it can then be as close as 12'.

DSCN9146_zpsd1f703ad.jpg


However, Edison will not change the drop unless I release the panel. Well it's not the original equipment and there is no permit for an upgrade.

DSCN9306_zpsf89451da.jpg


DSCN9308_zps10cef26f.jpg


The pool contractor has his head in the sand.
 
Where do you see 12'?

It is 22' in 680.8, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor up to 750v.

Otherwise 25'
 
gfretwell said:
Where do you see 12'? It is 22' in 680.8, Supported on and Cabled Together with a Solidly Grounded Bare Messenger or Solidly Grounded Neutral Conductor up to 750v.

Otherwise 25'
Here in California, we are forced to let the utility company make the rules.
 