1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Backflow Preventer Location

Discussion in 'Commercial Plumbing Codes' started by Mech, Dec 5, 2017.

  1. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    718
    Likes Received:
    10
    2009 IPC

    Three proposed buildings on one parcel in PA, which all will be fed from a common street tap.

    Is there a code requirement that each building has its own backflow preventer instead of one common bfp for all 3 buildings in the exterior meter pit? I did not find anything in Section 608, except that the potable water system must be protected.

    Thanks
     
  2. VillageInspector

    VillageInspector Sawhorse

    Joined:
    Feb 9, 2010
    Messages:
    58
    Likes Received:
    9
    I would require each building to have its own back flow preventer
     
  3. Msradell

    Msradell Sawhorse

    Joined:
    Jul 23, 2011
    Messages:
    754
    Likes Received:
    59
    I think code would allow you to just have one because the purpose is to protect the water system. In reality I agree with Villageinspector I would definitely prefer having one for each residence.
     
  4. JBI

    JBI Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,732
    Likes Received:
    262
    Would you want your water contaminated by your neighbor's?
    I also would require one for each building.
     
    my250r11, Pcinspector1 and cda like this.
  5. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,739
    Likes Received:
    539
    Back-flow prevention is not normally required for an entire building . They are required for certain fixtures and systems (fire sprinklers) where cross contamination may occur. That is why you can not find the answer to your question within the codes.
     
  6. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,387
    Likes Received:
    223
    Mech,

    Just a bit curious how that's being done, are the buildings daisy chained or will there be three individual lines exiting one meter pit?
     
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,654
    Likes Received:
    836

    Back flow at entry to property?

    Loop for fire hydrants and domestic?

    Tap off that loop to run to each building ??
     
  8. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,387
    Likes Received:
    223
    Is this is looped, is it done in the city utility easement or on private property?
     
  9. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,411
    Likes Received:
    569
    residential or commercial?
     
  10. tmurray

    tmurray Sawhorse

    Joined:
    Jun 10, 2011
    Messages:
    1,370
    Likes Received:
    314
    I think they are talking about connection to a public utility, which generally would require backflow protection to ensure that a loss of pressure in the main does not siphon contaminated liquid back into the main, resulting in contamination spreading to adjacent buildings/properties. But for private wells, yes you would be correct in that case.

    We would require each building to have a backflow preventer. If there is a backflow preventer on the main to the property, this arrangement increases the chances substantially that a loss in pressure in the main will cause cross contamination between the buildings once water pressure is restored.
     
    JBI likes this.
  11. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    718
    Likes Received:
    10
    Wow, lots of comments and follow up questions! Thanks.

    All buildings are commercial - a parking garage, a medical office building, and an apartment building. The MOB at the moment only has restrooms, a mop sink, and water fountains.

    The water is from a public water system.

    The civil engineer's plans show one meter pit w/ backflow preventer at the entry to the property and then one common supply line, not looped, that each building taps off of (daisy chained). The buildings do not have their own water line back to the meter pit.

    The fire suppression line has its own connection to the public water system, and then all three buildings daisy chain off that one supply line. I believe each building will have its own bfp for fire suppression; I am not concerned with this arrangement as I am not responsible for fire suppression.

    I am responsible for only the medical office building. There is at least one, if not two, other plumbing professionals responsible for the other two buildings.

    I would prefer each building receive its own bfp.

    If the code's intent is to protect the city's system, then the design has done so. If the code's intent is to provide protection between buildings, then this design fails.
     
  12. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,739
    Likes Received:
    539
    Do not leave the BFP requirements up to the fire guys. The plumbing code up dictates the type of BFP that is required depending on the system. My experience is the fire guys only look to see if one is installed not what type to use for a specific system. Two different ASSE standards

    Barometric loop
    High or low hazard
    Backsiphonage only
    (See Section 608.13.4)
    Double check backflow prevention
    assembly and double check fire
    protection backflow prevention assembly

    Low hazard
    Backpressure or backsiphonage
    Sizes 3/8² –16²
    ASSE 1015, AWWA C510, CSA B64.5, CSA B64.5.1


    Double check detector fire protection
    backflow prevention assemblies
    Low hazard
    Backpressure or backsiphonage
    (Fire sprinkler systems)

    Sizes 2²–16²
    ASSE 1048
     
  13. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,654
    Likes Received:
    836



    Does the city have any local requirements ???
     
  14. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,414
    Likes Received:
    98
    Not required per the IPC. But may be required by local code or utility company.
     
  15. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,539
    Likes Received:
    200
    $ * $

    Mech,

    Check with the State of Pennsylvania, Health Department,
    or whomever writes the "water protection" laws for the state.
    A bfp may not even be required for your 3 bldgs.

    I agree that it is a good idea to protect all 3 from each other,
    but is it required by "the powers that be" in PA ?......Some
    states have decided that a business occupancy and residences
    are considered a "Low Hazard" and therefore, ...no protection
    is required.

    Also, will your 3 bldgs. have Commercial Lawn Sprinkling
    systems installed ?.........These type systems can introduce
    chemicals in to the potable water system and cross contamination
    is a real concern.......Again, check with the State of PA and the
    current laws and regs........They may leave it up to each
    jurisdiction to decide, or they may have "across the board"
    Laws and regulations that apply to the whole state.



    $ * $
     
  16. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,427
    Likes Received:
    386
    Section 608.1


    608.1 General. A potable water supply system shall be


    designed, installed and maintained in such a manner so as to

    prevent contamination from nonpotable liquids, solids or

    gases being introduced into the potable water supply through

    cross-connections or any other piping connections to the system.

    Backflow preventer applications shall conform to Table

    608.1, except as specifically stated in Sections 608.2 through

    608.16.10.
     
    JBI likes this.
  17. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    5,739
    Likes Received:
    653
    Set by the water purveyor here....
     
  18. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    718
    Likes Received:
    10
    Sprinkler BFP will be per the Sprinkler contractor. I do not get a say in the matter. They have their own tap into the street. Potable water gets its own tap into the street.

    Not sure if the locals have their own requirement for BFP or not. I've been putting out fires on other projects and have not had time to contact the municipality.

    As stated above by mtlogcabin and Rick18071, a BFP is not required for the building and fatboy listed the code section that only requires the water system to be protected. All the projects I work on, I specify a BFP, so I never get a comment during code review stating a BFP is required.

    The company that contracted me did not mention irrigation, so my building will not get lawn sprinklers. If they tell me later they want irrigation, I will be giving them a separate BFP. They may be tapping for irrigation in the outside meter / BFP vault.

    There is no drain piping shown discharging from the meter / BFP vault. Once they figure out a vault drain is needed, we might be getting separate BFPs.
     
    JBI likes this.
  19. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    718
    Likes Received:
    10
    I spoke to the water authority today. They are OK with one double check valve in the meter pit protecting the three buildings on site. The Medical Office Building I am working on has two unfinished floors. Per the water authority, if an X-ray machine is added, blood is drawn, or sutures are administered, then this building requires an RPZ BFP, which cannot be installed in the meter pit.
     
  20. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,654
    Likes Received:
    836
    So an x ray machine pollutes the water,,,

    Interesting
     