    Dismiss Notice
    Dismiss Notice
Backflow Preventer Location
Discussion in 'Plumbing Codes' started by Mech, Dec 5, 2017.
  1. Mech
    Mech Sawhorse
    Oct 30, 2009
    733
    11
    2009 IPC
    Three proposed buildings on one parcel in PA, which all will be fed from a common street tap.
    Is there a code requirement that each building has its own backflow preventer instead of one common bfp for all 3 buildings in the exterior meter pit? I did not find anything in Section 608, except that the potable water system must be protected.
    Thanks
  2. VillageInspector
    VillageInspector Sawhorse
    Feb 9, 2010
    68
    13
    I would require each building to have its own back flow preventer
  3. Msradell
    Msradell Sawhorse
    Jul 23, 2011
    789
    71
    I think code would allow you to just have one because the purpose is to protect the water system. In reality I agree with Villageinspector I would definitely prefer having one for each residence.
  4. JBI
    JBI Sawhorse
    Oct 17, 2009
    2,772
    272
    Would you want your water contaminated by your neighbor's?
    I also would require one for each building.
    my250r11, Pcinspector1 and cda like this.
  5. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,995
    680
    Back-flow prevention is not normally required for an entire building . They are required for certain fixtures and systems (fire sprinklers) where cross contamination may occur. That is why you can not find the answer to your question within the codes.
  6. Pcinspector1
    Pcinspector1 Platinum Member
    Oct 28, 2009
    2,657
    288
    Mech,
    Just a bit curious how that's being done, are the buildings daisy chained or will there be three individual lines exiting one meter pit?
  7. cda
    cda Sawhorse
    Oct 19, 2009
    15,317
    919
    Back flow at entry to property?
    Loop for fire hydrants and domestic?
    Tap off that loop to run to each building ??
  8. Pcinspector1
    Oct 28, 2009
    2,657
    288
    Is this is looped, is it done in the city utility easement or on private property?
  9. ICE
    ICE Sawhorse
    7,812
    728
    residential or commercial?
  10. tmurray
    tmurray Sawhorse
    Jun 10, 2011
    1,454
    347
    I think they are talking about connection to a public utility, which generally would require backflow protection to ensure that a loss of pressure in the main does not siphon contaminated liquid back into the main, resulting in contamination spreading to adjacent buildings/properties. But for private wells, yes you would be correct in that case.
    We would require each building to have a backflow preventer. If there is a backflow preventer on the main to the property, this arrangement increases the chances substantially that a loss in pressure in the main will cause cross contamination between the buildings once water pressure is restored.
    JBI likes this.
  11. Mech
    Mech Sawhorse
    Oct 30, 2009
    733
    11
    Wow, lots of comments and follow up questions! Thanks.
    All buildings are commercial - a parking garage, a medical office building, and an apartment building. The MOB at the moment only has restrooms, a mop sink, and water fountains.
    The water is from a public water system.
    The civil engineer's plans show one meter pit w/ backflow preventer at the entry to the property and then one common supply line, not looped, that each building taps off of (daisy chained). The buildings do not have their own water line back to the meter pit.
    The fire suppression line has its own connection to the public water system, and then all three buildings daisy chain off that one supply line. I believe each building will have its own bfp for fire suppression; I am not concerned with this arrangement as I am not responsible for fire suppression.
    I am responsible for only the medical office building. There is at least one, if not two, other plumbing professionals responsible for the other two buildings.
    I would prefer each building receive its own bfp.
    If the code's intent is to protect the city's system, then the design has done so. If the code's intent is to provide protection between buildings, then this design fails.
  12. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,995
    680
    Do not leave the BFP requirements up to the fire guys. The plumbing code up dictates the type of BFP that is required depending on the system. My experience is the fire guys only look to see if one is installed not what type to use for a specific system. Two different ASSE standards
    Barometric loop
    High or low hazard
    Backsiphonage only
    (See Section 608.13.4)
    Double check backflow prevention
    assembly and double check fire
    protection backflow prevention assembly
    Low hazard
    Backpressure or backsiphonage
    Sizes 3/8² –16²
    ASSE 1015, AWWA C510, CSA B64.5, CSA B64.5.1
    Double check detector fire protection
    backflow prevention assemblies
    Low hazard
    (Fire sprinkler systems)
    Sizes 2²–16²
    ASSE 1048
  13. cda
    cda Sawhorse
    Oct 19, 2009
    15,317
    919
    Does the city have any local requirements ???
  14. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,601
    142
    Not required per the IPC. But may be required by local code or utility company.
  15. north star
    north star Sawhorse
    Oct 19, 2009
    3,634
    213
    Mech,
    Check with the State of Pennsylvania, Health Department,
    or whomever writes the "water protection" laws for the state.
    A bfp may not even be required for your 3 bldgs.
    I agree that it is a good idea to protect all 3 from each other,
    but is it required by "the powers that be" in PA ?......Some
    states have decided that a business occupancy and residences
    are considered a "Low Hazard" and therefore, ...no protection
    is required.
    Also, will your 3 bldgs. have Commercial Lawn Sprinkling
    systems installed ?.........These type systems can introduce
    chemicals in to the potable water system and cross contamination
    is a real concern.......Again, check with the State of PA and the
    current laws and regs........They may leave it up to each
    jurisdiction to decide, or they may have "across the board"
    Laws and regulations that apply to the whole state.
  16. fatboy
    fatboy Administrator
    Oct 17, 2009
    5,558
    457
    Section 608.1
    608.1 General. A potable water supply system shall be
    designed, installed and maintained in such a manner so as to
    prevent contamination from nonpotable liquids, solids or
    gases being introduced into the potable water supply through
    cross-connections or any other piping connections to the system.
    Backflow preventer applications shall conform to Table
    608.1, except as specifically stated in Sections 608.2 through
    608.16.10.
    JBI likes this.
  17. steveray
    steveray Sawhorse
    Nov 25, 2009
    6,070
    750
    Set by the water purveyor here....
  18. Mech
    Mech Sawhorse
    Oct 30, 2009
    733
    11
    Sprinkler BFP will be per the Sprinkler contractor. I do not get a say in the matter. They have their own tap into the street. Potable water gets its own tap into the street.
    Not sure if the locals have their own requirement for BFP or not. I've been putting out fires on other projects and have not had time to contact the municipality.
    As stated above by mtlogcabin and Rick18071, a BFP is not required for the building and fatboy listed the code section that only requires the water system to be protected. All the projects I work on, I specify a BFP, so I never get a comment during code review stating a BFP is required.
    The company that contracted me did not mention irrigation, so my building will not get lawn sprinklers. If they tell me later they want irrigation, I will be giving them a separate BFP. They may be tapping for irrigation in the outside meter / BFP vault.
    There is no drain piping shown discharging from the meter / BFP vault. Once they figure out a vault drain is needed, we might be getting separate BFPs.
    JBI likes this.
  19. Mech
    Mech Sawhorse
    Oct 30, 2009
    733
    11
    I spoke to the water authority today. They are OK with one double check valve in the meter pit protecting the three buildings on site. The Medical Office Building I am working on has two unfinished floors. Per the water authority, if an X-ray machine is added, blood is drawn, or sutures are administered, then this building requires an RPZ BFP, which cannot be installed in the meter pit.
  20. cda
    cda Sawhorse
    Oct 19, 2009
    15,317
    919
    So an x ray machine pollutes the water,,,
    Interesting
Share This Page