• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

Bollards & Means of Egress

Alias

REGISTERED
Joined
Oct 26, 2009
Messages
1,649
Location
State of Disbelief
"CBC Section 1133B.5.2 - Width - Ramps shall have a minimum clear width of 48' (1219mm), unless required to be wider by code."

So, I stopped at the new USFS building yesterday and found that bollards are being installed directly in front of the two front doors and in the ramp leading to the rear parking lot. The rear bollards interior edge to interior edge are 40" apart.

O-------O (bad diagram)

<- 40" ->

As the bollards will constrict exiting to the rear parking lot, are the bollards spaced correctly? Is it 48" center to center or 48" edge to edge"? Front bollards appear even closer together.

Concrete for bollards hasn't been poured yet, hence the question.

Sue
 
I treat them the same as doorways and they must be at least 32 inches (clear) apart with total clear width provided for egress
 
"Minimum clear width" should be the minimum clear distance between the bollards. Kind of like "not less than".
 
Thanks, my thoughts exactly. I just looked at the civil plans and it shows 4' o.c. Off to talk to owner before he pours concrete.

Sue
 
= =



" ...and found that bollards are being installed directly in front ofthe two front doors and in the ramp leading to the rear parking lot."
48 inches of clearance required between the innermost edges.

= =
 
What is the purpose of the bollard? Likely a barrier against vehicular entry into the building. A security feature.

I don't have a plan, so I cannot understand your reference to a ramp. Commonly, this feature is frequently installed forward of retail stores along the front sidewalk at the curb ramp. Is this a curb ramp?

Now there is a concern to have some width, but not too much, to maintain things from a security pov. Could a mini fit through?

But also, consider that the once can go or get around the bollard. It typically doesn't form a wall.

And while you may need to have an egressable route (on may argue if it applies or not), this doesn't mean all instances of these would have to be like separated. Just where it is necessary.

Essentially the bollard is a framed opening.
 
Minimum clear width of 48"

The average dimension for the width of a car is about six feet

four feet will stop it
 
We are still at 36" clear here per Ansi 117 and IBC.....make sure they have room for the handrails inside those bollards...sounds like 48"OC will still not be enough for you CA types...
 
From the OP and from the discussion I don't think handrails come into play in this case. Unless there's a drop-off on either side of the ramp (or sidewalk) there's no need for handrails!
 
Msradell said:
From the OP and from the discussion I don't think handrails come into play in this case. Unless there's a drop-off on either side of the ramp (or sidewalk) there's no need for handrails!
A sloped floor would not need handrails....a ramp would.....
 
In CA 36" is okay

STA2010082314383270135.jpg
 
Back
Top