• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Brewery & taproom with interior mezzanine level or exterior raised platform

Brian Wallace

Registered User
Joined
Oct 30, 2018
Messages
1
Location
Charlotte, NC
North Carolina

Buildings:
Taproom - 1300 sf
Brewhouse - 4200 sf (with 22' ceilings and possibility of mezzanine level)
Exterior Beer Garden - 3,000 sf

*Dining/drinking area will include the taproom as well as the beer garden.

Scenerio #1:
We want to build an elevated exterior patio approximately 16' above finished grade with the possibility of an additional level. The area below the elevated concrete deck will be usable and not enclosed.

Q. Would we be required to install a lift or elevator if we chose to add a second level to this structure? If we need to reduce the total square footage in order to not install an elevator we would be open to it.

** Note - This elevated patio is to increase beer garden square footage. The skyline is easily visible from the ground level. No additional services would be offered that are not offered in accessible areas.

Scenerio #2:
Instead of a free standing structure with concrete decks we would stack shipping containers several levels high and utilize the roof of some of the containers as small private patios.

Q. If we stack two containers we would effectively end up with two floors with a rooftop level (also a floor?). Does this require a lift or elevator?

** Same note as above

Do 1108.2.4 Exceptions relate to this issue?

Any help would be much appreciated.


Cheers,
 
Welcome

Sounds like a nice concept either way

Give it a day or two for responses

Are you near the coast line??
 
Scenario #1: OK as long as the different non-accessible levels are less than 3.000 sq. ft. total, have the same services as an exterior accessible level and meets exception #2:

2. In multilevel assembly seating areas where the
second floor or mezzanine level provides 25 percent
or less of the total seating capacity and 300
or fewer seats, all wheelchair spaces shall be permitted
to be located on the main level.

Scenario #2: Good luck in having an engineer designing it.
 
2010 ADASAD 206.2.5 Restaurants and Cafeterias. In restaurants and cafeterias, an accessible route shall be provided to all dining areas, including raised or sunken dining areas, and outdoor dining areas.
EXCEPTIONS:
2. In alterations, an accessible route shall not be required to existing raised or sunken dining areas, or to all parts of existing outdoor dining areas where the same services and decor are provided in an accessible space usable by the public and not restricted to use by people with disabilities.
 
2015 IBC 1108.2.9 Dining and drinking areas. In dining and drinking areas, all interior and exterior floor areas shall be accessible and be on an accessible route.
Exceptions:
2. An accessible route to dining and drinking areas in a mezzanine is not required, provided that the mezzanine contains less than 25 percent of the total combined area for dining and drinking and the same services, and decor are provided in the accessible area.
 