• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Ceiling or attic joists on hangers R802.6 Bearing

Yes.. that is a basic ledger connection.

R802.6 Bearing
The ends of each rafter or ceiling joist shall have not less than 11/2 inches (38 mm) of bearing on wood or metal and not less than 3 inches (76 mm) on masonry or concrete. The bearing on masonry or concrete shall be direct, or a sill plate of 2-inch (51 mm) minimum nominal thickness shall be provided under the rafter or ceiling joist. The sill plate shall provide a minimum nominal bearing area of 48 square inches (30 865 mm2).
 
Depends how the 2x8 is fastened to the gable studs. I would definitely flag it on inspection, unless an engineer designed it that way. As for being a basic ledger connection, I would disagree since the ledger board is not fastened to rim joist as the IRC shows for deck connections. I am not aware of any prescriptive way to ledger to studs.

The Simpson hangers certainly comply with the 1 1/2" bearing on metal that classicT quoted.

classicT, are you looking at a section for ledgers that I have not seen?
 
Depends how the 2x8 is fastened to the gable studs. I would definitely flag it on inspection, unless an engineer designed it that way. As for being a basic ledger connection, I would disagree since the ledger board is not fastened to rim joist as the IRC shows for deck connections. I am not aware of any prescriptive way to ledger to studs.

The Simpson hangers certainly comply with the 1 1/2" bearing on metal that classicT quoted.

classicT, are you looking at a section for ledgers that I have not seen?
This is not a deck, so forget what the ledger provisions are for a deck. Not sure why you would go there.

The section that I quoted was the specific code section that they asked about. So my answer addressed their specific question.

As for not knowing about prescriptive ledgers, try taking a look at IRC Table 602.3(1). The following image is from said table and gives prescriptive ledger requirements.
1640889706471.png
 
Looks like a form of balloon framing unless I'm missing something?

You could have a hinge at the double plates depending on the sheeting overlap or if some metal straps are being used?
 
1640889706471.png
Awesome, thank you! First time I had seen that.
 
Here is a photo. The top plates are over a header here. Some osb attic floor is on the joist. Ceiling joists are connected on both sides of the house in this fashion. Rafters run perpendicular to these joists

 
So bigger question is, with a stick framed roof, how are the ceiling joists perpendicular to the rafters? Most commonly, the ceiling joists act as the rafter ties, preventing the outward spread (overturning) of the exterior walls. Are there rafter ties above the ceiling joists (unlikely) or is the ridge formed by a ridge beam (thus no collar or rafter ties required)?

1640893369658.png
 
Ok. There was 1 photo on my camera that showed the roof detail but it was in a shadow. I was able to lighten the image on photoshop. It looks like a ridge board up there. I honestly was not sure as have only looked at the house a few times.

 
Ok. There was 1 photo on my camera that showed the roof detail but it was in a shadow. I was able to lighten the image on photoshop. It looks like a ridge board up there. I honestly was not sure as have only looked at the house a few times.

Image isn't clear enough to tell if it is a ridge beam or a ridge board, and it doesn't appear to be the same roof anyways. The first photo had 2x4 ceiling joists and this photo has a framed floor.
 
Was able to get some better images. The gable studs are 2x6 and the old lower wall studs are 2x4.









 
1640917177019.jpeg

Solid, full depth blocking between the studs would have provided the opportunity to nail the ledger and transfer the load to the wall top plate.
 
Last edited:
1640917492739.jpeg

That is a ridge board….not a beam….a rafter tie is mentioned in the code. The sheathing came up short…. but hey now….a ridge vent will justify that.
 
Last edited:
1640917661492.jpeg

Solid blocking between the joists over the wall and a proper header at the opening could make a difference….well that’s what I would have done….I tend to over build.
 
Last edited:
Thanks for the replies, it all helps. I am making notes of what this might need to get a certificate of occupancy so all commentary is appreciated. Fire blocking, rafter ties, I am listing as needed. It sounds like the ceiling joist design is ok. There are a few collar ties in at the other end of the roof and a lot of other incomplete work --- this place was sold as-is.
 
All of what Ice mentioned, and then some. I also see a possible missing header, missing nails in the hangers, and just questionable methods overall. I think you need to get a qualified and experienced framer involved ASAP.
 
Any thoughts? Can the load of the the joists be "transferred to the wall top plate"?
Or reinforced any other way? Thanks

1640917177019-jpeg.8467
 