• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Change of occupancy and relative hazard classification

pmarx

Bronze Member
Joined
Oct 13, 2010
Messages
114
I'll try posting this again but in the proper forum.

For purposes of discussion, an existing six story building:

1st Fl
Existing Use B (4) Proposed Use B (4)
2nd Fl
Existing Use M (3)/B (4) Proposed Use A-2 (3), A-3 (3), M (3), R-1 (3)
3rd Fl
Existing Use B (4), R-2 (3) Proposed Use R-1 (3)
4th Fl -6th Fl
Existing Use R-2 (3) Proposed Use R-1 (3)


These are relating to Table 1012.4 by way of example. Does the fact that, in total, no proposed use is to a higher hazard then currently exists mean that the change of use can be considered as a change to an equal or lower hazard category for purposes of evaluating 1012.4, 1012.5 and 1012.6?
 
See response to other post - also you can do partial changes of occupancy within a building if you desire - if not, then the entire building would have to be reclassified to the highest hazard or most restrictive requirements- Not any different than in a new building allowing you to use separated or non- separated provisions of the building code.
 