• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Combustible foam on exterior wall/roof near property line

Ryan Schultz

Registered User
Joined
Apr 2, 2012
Messages
266
Location
Madison, WI
In the scenario below, possible to use EPS or Polyiso on the roof? I assume it is if it meets 2603.6 Roofing

Possible to use EIFS on that 1st floor wall? I assume it is because of 2603.4 Thermal Barrier. That is, the concrete acts as the the 'thermal barrier'.


code%20question%20on%20wall%20ratings.jpg
 
EIFS can be used on any construction, since it is required to be tested per NFPA 285 as part of its compliance with ASTM E2568 per IBC Section 1408.2. The concrete is sufficient as a thermal barrier for the wall to comply with 2603.4. It will have to be part of a 2-hour tested assembly, though, for exposure on both sides.

Foam insulation can be used on a roof as long as it is covered by an approved roof covering and complies with either NFPA 276 or UL 1256 when tested as an assembly per IBC Section1508.1 and Section 2603.4.1.5, Item 2.

The issue I have is how can you have a Group S-1 in Type IB construction below a Group R-2 in Type VB construction with only a 2-hour horizontal assembly?
 