indyarchyguy
In a corridor of an office building (B-Occupancy), the corridor width minimum requirement by code is 44-inches (Table 1018.2). Based on occupancy the calculated width of the corridor needs to be at least 39-inches. Therefore a 44-inch minimum width is acceptable. The ACTUAl corridor width is 60-inches. Along one side of the corridor the pilasters around the structural columns are 5-1/2-inches in depth. Thereby reducing the actual egress width down to 54-1/2-inches. This is still wider than the minimum requirement of 44-inches. Does the 2012 IBC, Sec. 1003.3.3 make this corridor non-compliant because the pilaster exceeds 4-inches?
"1003.3.3 Horizontal Projections
Structural elements, fixtures or furnishings shall not project horizontally from either side more than 4 inches (102 mm) over any walking surface between the heights of 27 inches (686 mm) and 80 inches (2032 mm) above the walking surface."