Industrial project with large "U" shaped conveyor equipment (continuous).
F-2 occupancy, fully-sprinklered.
7'-0" wide conveyor X +/- 600' long (300' each side of "U").
7'-0" aisle between each leg of "U".
---
Plan review resulted in comment pertaining to 100' requirement of 1014.3, Exception #1. Building Official will not allow equipment to be used unless it is re-designed to accommodate required exit access/CPET.
Equipment is specialized/customized design.
Personnel will need to be within "U" for short periods of time for maintenance/inspection purposes.
Thoughts?
Thanks.