• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

CRC/CBC 312.1.1

Mateo001

Registered User
Joined
Jan 16, 2021
Messages
14
Location
Monterey county
Please render your opinion if this raised concrete balcony is compliant with 2016 CRC and CBC 312.1.1.

312.1.1:
Guards shall be provided for those portions of open-sided walking surfaces, including stairs, ramps and landings, that are located more than 30 inches measured vertically to the floor or grade below at any point within 36 inches horizontally to edge of open side.

312.1.2:
Required guards at open-sided walking surfaces, including stairs, balconies or landings, shall be not less than 42 inches in height as measured vertically above adjacent walking surface or the line connecting the nosings.


Raised concrete balcony

1610861864990.jpeg




-18” tall boundary wall on balcony.
-51” from top of boundary wall to top of planter box.
-70” from top of boundary wall to concrete driveway and to bottom of empty planter.
-Planter box width 30” from edge of open side
1610861911967.jpeg

1610861911967.jpeg1610862107214.jpeg
1610862418323.jpeg
 
you are mixing the commercial code and the 1 & 2 family code,
You are under the 1 & 2 family code your guard needs to be 36 inches tall and depending on the edition you are under the hight above the fixed seats changes s
 
you are mixing the commercial code and the 1 & 2 family code,
You are under the 1 & 2 family code your guard needs to be 36 inches tall and depending on the edition you are under the hight above the fixed seats changes
Commish: Yes, you’re right, this is single family residential so CRC would apply. I only placed IRC diagram for reference of code intent. The height requirement for guardrail for CRC would be 42”. My question to everyone is, please tell me if it is compliant with CRC and if so/not explain.
 
Guards shall be provided in accordance with Sections R312.1.1 through R312.1.4.
2019 CRC R312.1.1 Where Required
Guards shall be provided for those portions of open-sided walking surfaces, including stairs, ramps and landings, that are located more than 30 inches (762 mm) measured vertically to the floor or grade below at any point within 36 inches (914 mm) horizontally to the edge of the open side. Insect screening shall not be considered as a guard.
2019 CRC R312.1.2 Height
Required guards at open-sided walking surfaces, including stairs, porches, balconies or landings, shall be not less than 42 inches (1067 mm) in height as measured vertically above the adjacent walking surface or the line connecting the nosings.

No your proposal does not meet the code, without additional rails or other barrier.


1610980815164.png
 
Last edited:
Guards shall be provided in accordance with Sections R312.1.1 through R312.1.4.
2019 CRC R312.1.1 Where Required
Guards shall be provided for those portions of open-sided walking surfaces, including stairs, ramps and landings, that are located more than 30 inches (762 mm) measured vertically to the floor or grade below at any point within 36 inches (914 mm) horizontally to the edge of the open side. Insect screening shall not be considered as a guard.
2019 CRC R312.1.2 Height
Required guards at open-sided walking surfaces, including stairs, porches, balconies or landings, shall be not less than 42 inches (1067 mm) in height as measured vertically above the adjacent walking surface or the line connecting the nosings.

No your proposal does not meet the code, without additional rails.
Thank you, Mark Handler. I appreciate your input.
 
Comish
I cited the California Codes
California has you beat for the odd and unique modifications to the model codes.
 