1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Dead end corridor within mixed occupancies

Discussion in 'Commercial Building Codes' started by tuzi, Jul 24, 2018.

  1. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    I have a floor plate with R2, S-2, and A-2. The aggregate area of S-2 and A-2 are over 10% of the floor plate. If I take the floor as un-separated occupancies, then I know I have to follow 20' dead end as A-2 is the more stringent. I am wondering if I separate A-2 from the rest of the floor with 1-hour fire barrier with 45 min. door, does it mean max. 50' dead end corridor for R-2 will apply or it's not the case unless aggregate area of S-2 and A-2 is under 10%?
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,347
    Likes Received:
    356
    If a corridor is serving an assembly occupancy, then you're limited to the 20-foot limit on dead-end corridors, regardless of whether or not the assembly occupancy is an accessory use. Accessory uses are still classified per the applicable occupancy group, the main exception is that you do not have to separate the accessory occupancies from the main occupancy, but all other code provisions applicable to those accessory occupancies are still required.
     
  3. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    [​IMG]
    The corridor I circled only serves the R2, does it mean it could be max. 50 ft, although I have A-2 on this level?
     
  4. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,347
    Likes Received:
    356
    The image didn't come through, but if the corridor is only serving the Group R, then yes, the longer distance for a dead end corridor would be permitted.
     
  5. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
  6. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866

    You either have to be a paying Sawhorse to post direct

    Or turn it into a link and post the link
     
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    While waiting for the floor plan.

    Where your concern is with the dead end,

    Are you required two means of exit ??
     
  8. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    Add a door across the corridor in the dead end.

    Not sure if you put it on a mag door holder, if it is still legal????
     
  10. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    That's what I did now, but I just wonder if code allows without the door.
     
  11. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866

    So what is the measurement of the dead end??
     
  12. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    [​IMG]


    I am at 48'-6". I can reduce it to under 20' by adding a door in the corridor.
     
  13. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    Which edition of IBC?
     
  14. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    Looks like as said by RGLA

    Corridor used by assembly

    20 ft max or widen the dead end portion
     
  15. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    2015IBC
     
  16. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    Yeah, I think I need to add the door.

    Thanks, everybody for helps!
     
  17. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866

    You know you can become a Sawhorse and support this great site

    We have the unlimited plan, keep asking questions till you get an answer you like!!!
     
  18. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,913
    Likes Received:
    235
    Why can't you shift the doorways 20 feet forward and increase the apartment square footage?
     

    Attached Files:

  19. tuzi

    tuzi Registered User

    Joined:
    Jun 14, 2016
    Messages:
    40
    Likes Received:
    4
    I guess that is possible, too. Thanks,
     
  20. mtlogcabin

    mtlogcabin Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    6,808
    Likes Received:
    568
    I assume the entire building is sprinkled so you get the 125 ft of common path of travel that would be permitted and not the 75 ft limit without sprinklers
     