• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Door mullion?

Hi Michael -

There is no prohibition on mullions in a means of egress in an assembly occupancy as long as the minimum clear opening width requirement is met. So with the door open to 90 degrees, you need at least 32 inches between the face of the door and the side of the mullion.
 
Lgreene,
Thanks. Load calculation only requires one 3'-0" but would like to use a pair of 3'0" doors with a removable mullion just as a convenience to move items in and out if needed.
 