1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Door operator button question

Discussion in 'Accessibility' started by CAR, Oct 8, 2019.

  1. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    A Milwaukee client currently has these buttons on their elevator lobby going into their suite. They are asking us if they could replace this button a blank button (not engraved) and reword the nearby signage to say 'push for emergency', instead of 'push to exit'. I can't find on the requirements online if the button itself needs to be labeled or engraved or if it can be blank with adjacent signage. Has anyone come across this before? Thank you.
     

    Attached Files:

  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071
    So what happens when you push the button???

    door opens

    mag lock releases

    other

    Does the elevator lobby have the one required exit, available to anyone???
     
  3. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    460
    Likes Received:
    110
    So you step out of the elevator cab, into the elevator lobby, and you have to push this button to enter their suite? If thats correct, then the button has no impact on exiting the building ... right?
     
  4. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    That's my interpretation. Pasting her question below:

    "We are considering updating the face plates on these push to exit buttons. They allow people to enter our suites without swiping their access card. The plan is to install a blank face plate and reword the nearby signage to say push for emergency, instead of push to exit. Do you know if this button must have specific verbiage required by code?"
     
  5. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071
    Hum

    seems like a little confusing

    not sure why “push for emergency”???


    But once again, step off elevator, does everyone have unrestricted access to at least one exit???

    or is this button needed to get to the one exit??
     
  6. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    OK, so I'm not the only one confused. I'll have to clarify with her. Because the way I see it, there shouldn't be an egress issue going in. But why would you push for emergency going against egress. I re read it and something doesn't make sense. I'll clarify once I know more. Thank you all for the quick replies.
     
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071
    I have seen a by pass button, to basically override a card reader.
     
  8. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    That's what it looks like to me. What's confusing is the "push for emergency" verbiage that's throwing me off.
     
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071
    Sounds like they might not have code complying exit system.
     
  10. ADAguy

    ADAguy Sawhorse

    Joined:
    Sep 11, 2013
    Messages:
    3,795
    Likes Received:
    361
    Inquiring minds await your response.
     
  11. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,013
    Likes Received:
    114
    Is there an exit available to the elevator lobby without going into the tenant space?
     
  12. e hilton

    e hilton Bronze Member

    Joined:
    Jul 2, 2014
    Messages:
    460
    Likes Received:
    110
    That’s my current thought, after having slept on it. I bet there are compliant stairs, but they are not accessible from the lobby ... you have to enter the suite to use them.
     
  13. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,013
    Likes Received:
    114
    That is the only time I see this type of button used. Essentially the tenant space is not secure as it needs to be available for exiting from the elevator lobby.
     
  14. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    OK, I see now how their existing is a little different than usual because they have to go into their suite to access stairs (image below). As mentioned before this is an existing condition. Looking online I see they make 'blank' buttons. But I still can't find anything specific about the button having to be engraved or if an adjacent sign is acceptable.

    I can always ask the City to see how they interpret this. They may have an interpretation or just refer me back to ADA, as it is a Civil Rights law and not a code per-se. They have been pretty good I the past, about providing clear direction.
     
  15. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071
    Hum

    so the city approved exiting that does not meet code


    Seems like there should be a big sign

    “””Push button to access exit stair”””””

    I would not approve a blank or change any wording, that indicates if you want to exit do this.

    This is not an ada issue,,

    Plus you should tell the business they may be liable if someone gets hurt, because a person cannot get to an exit.
     
  16. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,013
    Likes Received:
    114
    This is an exiting issue and not an ADA issue. The requirements for this type of exiting are very specific.
     
  17. CAR

    CAR Sawhorse

    Joined:
    Feb 14, 2019
    Messages:
    20
    Likes Received:
    0
    Ah, found it. Thank you everyone for your help!
     

    Attached Files:

  18. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    16,597
    Likes Received:
    1,071

    Yes and no

    It would be yes if in a code complying exit system.

    But, not sure if I would touch this, and not sure how this got approved along time ago.
     
  19. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    563
    Likes Received:
    158
    With out a plan view not sure, but is it possible to create a hallway to the Exit and add a door to the tenant space that has the card reader to that space?
     
  20. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    1,013
    Likes Received:
    114
    It is not that unusual of an exiting situation and the CBC is very specific about how to achieve. Typically you can never get a tenant to agree to essentially having their suite be unsecured at all times. Anyone can push the button and have access directly into and thru the tenant space at any time.
     