1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Drywall question

Discussion in 'Commercial Building Codes' started by pletzer28, Aug 7, 2013.

  1. pletzer28

    pletzer28 Member

    Joined:
    Feb 14, 2012
    Messages:
    15
    Likes Received:
    0
    Small new commercial woodworking shop 2640 sqft. Total with different rooms so non sprinkled. I am wondering code for celling drywall. Its on my state approved plans as 5/8 sheetrock. Building is in Wisconsin. I am I required to have double 5/8s on celling??

    Thanks
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    So you have state approved plans with one layer ?

    That should fly

    Why are you asking about another layer??
     
  3. pletzer28

    pletzer28 Member

    Joined:
    Feb 14, 2012
    Messages:
    15
    Likes Received:
    0
    Yes it just says 5/8 drywall w/ vapor barrier. points to ceiling and walls in drawing on multiple pages.

    Been getting asked by when getting quotes. Also neighbor guy that has drywall company said he had to have 2 layers at his shop but he had mezzanine above. I have raised cored truss and will blow r 50 in ceiling.

    thanks
     
  4. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    14,877
    Likes Received:
    866
    Unless you are required a rated assembly, you should be good to go.

    The approved plans give you a back up as long as they truly represent everything going on with the space and business
     
  5. fatboy

    fatboy Administrator

    Joined:
    Oct 17, 2009
    Messages:
    5,471
    Likes Received:
    407
    Agree with cda.
     
  6. kilitact

    kilitact Gold Member

    Joined:
    Oct 20, 2009
    Messages:
    722
    Likes Received:
    30
    This is an oldie, but have a similar scenario, wood shop/cabinet shop in excess of 2500 sq ft. This would appear to trigger the need for fire sprinklers of different fire areas?
     