JustReid
Bronze Member
2009 IBC - I have a 4 story building where the upper three levels are provided with elevator lobbies. The lobby on each floor segments the corridor essentially creating an “intervening room” (See attached sketch). It is a B occupancy and no corridor rating is required since it will be fully sprinklered. I am looking at requiring that doors be installed on the elevator openings to comply with 708.14.1 Exception 3 to provide the shaft protection required by 708.14. The proposed design was using the lobby enclosure as the shaft protection. However, since the lobby is essentially a part of the corridor and passing through this space subjects the occupants to a four story shaft, I think that these doors (or at least one of the other Exceptions to the elevator lobby) would be required. I don’t really see this as an intervening room issue but more as a shaft protection issue. Does anyone have any opinions on this? Or could maybe point out a specific code string that deals with this situation that I am overlooking? ThanksView attachment 1138